# Rockwell PLC Download - tags in browser are gone

**URL:** <https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306>\
**Category:** Ignition\
**Created:** [April 23, 2024, 5:05pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306 "2024-04-23T17:05:01Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![Jakub\_Zwolinski](https://avatars.discourse-cdn.com/v4/letter/j/3be4f8/32.png) [@Jakub\_Zwolinski](https://forum.inductiveautomation.com/u/Jakub_Zwolinski)\
**Post date:** [April 23, 2024, 5:05pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/1 "2024-04-23T17:05:01Z")

</div>

Hi there!

I got an really important very very high priority problem.  
We are using 2 Ignition gateways setup - one is out SCADA client, Second is our Software Gateway.  
Of course Rockwell PLC is connected to the Software Gateway via Logix driver.  
What happened today and is absolutely not explainable for me...  
I did a PLC change in studio 5000 - i have only added two not important rungs and then I did download.. AND SINCE THAT moment all the coomunication was ruined! I saw message that device Rockwell PLC is connected but when i went to the OPC Quick Client - there were not any single TAGS! The only thing i saw was the diagnostics section...  
It was fixed by me restoring all .gwbk file..  
WHAT have i did wrong.. ? WHY all the comms where gone just because i downloaded PLC ?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 23, 2024, 5:07pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/2 "2024-04-23T17:07:38Z")

</div>

Is the Ignition Logix driver for that PLC set to "auto browse" ? If **not** , a PLC download breaks it (changes all the optimization ID numbers for the tags).

If it **is** set to autobrowse, the traffic should recover within a minute or two of the download completion.

You almost certainly did **not** need to restore a gateway backup. Simply restarting a device connection on the Ignition side will force a rebrowse.

---

<div class="post-metadata">

**Author:** ![Jakub\_Zwolinski](https://avatars.discourse-cdn.com/v4/letter/j/3be4f8/32.png) [@Jakub\_Zwolinski](https://forum.inductiveautomation.com/u/Jakub_Zwolinski)\
**Post date:** [April 23, 2024, 5:09pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/3 "2024-04-23T17:09:10Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/a/ca2941c59e7b8fd663dbf4120742085316442545.png)

I think so.. it is set to autobrowse

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 23, 2024, 5:09pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/4 "2024-04-23T17:09:57Z")

</div>

How long did you wait before you panic'd ?

---

<div class="post-metadata">

**Author:** ![Jakub\_Zwolinski](https://avatars.discourse-cdn.com/v4/letter/j/3be4f8/32.png) [@Jakub\_Zwolinski](https://forum.inductiveautomation.com/u/Jakub_Zwolinski)\
**Post date:** [April 23, 2024, 5:10pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/5 "2024-04-23T17:10:00Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/e/be8e0003975c8631219244541c488ab3da570428.png)

And it is logix driver

---

<div class="post-metadata">

**Author:** ![Jakub\_Zwolinski](https://avatars.discourse-cdn.com/v4/letter/j/3be4f8/32.png) [@Jakub\_Zwolinski](https://forum.inductiveautomation.com/u/Jakub_Zwolinski)\
**Post date:** [April 23, 2024, 5:10pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/6 "2024-04-23T17:10:50Z")

</div>

I think a lot.. 5 minutes for sure..  
I already have used the Quick connect browser and nothing was there..

At least you do not decide to revive the whole system using \*gwbk in 30 sec.. it was longer time..

---

<div class="post-metadata">

**Author:** ![Jakub\_Zwolinski](https://avatars.discourse-cdn.com/v4/letter/j/3be4f8/32.png) [@Jakub\_Zwolinski](https://forum.inductiveautomation.com/u/Jakub_Zwolinski)\
**Post date:** [April 23, 2024, 5:15pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/7 "2024-04-23T17:15:28Z")

</div>

Maybe the solution is just the oposite you said.. if i know that I am not doing any major changes in tags.. why should i trigger rebrowsking.. maybe for the future.. i need to disable rebrowsing and tirgger it just when i am sure it is needed..

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 23, 2024, 5:17pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/8 "2024-04-23T17:17:03Z")

</div>

If the Logix driver failed to rebrowse, it may be a bug worth reporting. What specific version of Ignition is this?

---

<div class="post-metadata">

**Author:** ![Jakub\_Zwolinski](https://avatars.discourse-cdn.com/v4/letter/j/3be4f8/32.png) [@Jakub\_Zwolinski](https://forum.inductiveautomation.com/u/Jakub_Zwolinski)\
**Post date:** [April 23, 2024, 5:18pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/9 "2024-04-23T17:18:01Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/4/e45c31458ee24baa30a07aa18e08242f960dbd0e.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 23, 2024, 5:18pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/10 "2024-04-23T17:18:42Z")

</div>

Yeah, pretty old. I'm pretty sure Kevin has worked on the Logix driver since then.

---

<div class="post-metadata">

**Author:** ![Jakub\_Zwolinski](https://avatars.discourse-cdn.com/v4/letter/j/3be4f8/32.png) [@Jakub\_Zwolinski](https://forum.inductiveautomation.com/u/Jakub_Zwolinski)\
**Post date:** [April 23, 2024, 5:19pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/11 "2024-04-23T17:19:23Z")

</div>

Is it possible to update just the driver?  
Cause it is the client specific - i can't update whole Ignition?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 23, 2024, 5:26pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/12 "2024-04-23T17:26:24Z")

</div>

> [@Jakub\_Zwolinski](#):
>
> just the driver?

Not an IA driver, no. Those are tied to the platform version--you have to upgrade the whole thing.

That isn't true for 3rd party modules, like my alternate driver for Logix and related EtherNet/IP PLCs. You can run the latest version with platform 8.1.11:

> [@Automation Professionals' EtherNet/IP Communication Suite V2](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/158):
>
> Automation Professionals is pleased to announce a new production release, upgrading Producer/Consumer tag support and fixing a minor bug in Host driver JSON exports. For Ignition 8.1+: [v2.1.15.241031951](https://www.automation-pros.com/ignition/EthernetIP%20Class%201%20Communications-2.1.15.241031951-v81.modl) (Yes, I skipped 2.1.14. There was a private beta that wasn't good enough, and was overtaken by other developments.) Also, the producer/consumer tag support got a much-needed section of expanded documentation. See the Host Driver Application Notes, §6.3 and §6.4, in [the updated manual](https://www.automation-pros.com/enip1/UserManual.pdf).

---

<div class="post-metadata">

**Author:** ![earnhartj84](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/earnhartj84/32/29405_2.png) [@earnhartj84](https://forum.inductiveautomation.com/u/earnhartj84)\
**Post date:** [May 29, 2024, 2:01pm UTC](https://forum.inductiveautomation.com/t/rockwell-plc-download-tags-in-browser-are-gone/89306/13 "2024-05-29T14:01:21Z")

</div>

I see that this is a Trial version. Are you sure that when you made the download to the plc, the trial version didn't expire? That can also cause tags to stop responding to comms.  
I'm sure I'm wrong, but just noticed that.