Hello all,

I am new to the Seimens line of PLCs and I cannot get any values out of the S7 1200.

I have read through old posts and have tried all the things listed. I have set the PLC to “Full Acess”. I am using TIA Portal v13 to program the PLC.

I get a connected status in the Ignition Gateway. In Designer, my values are null. My addressing in Designer is:  
[S7 1200 PLC]IB0 – This should be the physical address of the physical inputs on the PLC.

The Gateway Console Error I get is:  
Error reading S7ReadResponse. Error code=8104

Windows 7  
Ignition 7.7.0  
Java 1.8.0\_11

If anyone could point me in the right direction, it would be much appreciated!  
Thanks,  
Greg

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 25, 2014, 5:07pm UTC](https://forum.inductiveautomation.com/t/seimens-s7-1200-communications/8916/2 "2014-08-25T17:07:16Z")

</div>

In addition to setting ‘full access’ you also must make sure that you check the box at the bottom of that dialog to enable PUT/GET communication from remote partner. On data blocks, ‘optimized block access’ must be unchecked as well.