# Server keeps dropping modbus connections to all plc's

**URL:** <https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216>\
**Category:** Ignition\
**Tags:** ignition78\
**Created:** [April 25, 2020, 4:42am UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216 "2020-04-25T04:42:57Z")\
**Posts on this page:** 17\
**Page:** 3

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 4:23pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/41 "2020-04-27T16:23:49Z")

</div>

Yeah, might be that time, hopefully I don’t get in trouble:)

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 5:12pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/42 "2020-04-27T17:12:55Z")

</div>

so modpolling from the server doesn’t work, but telnet does, any thoughts on that

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 5:18pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/43 "2020-04-27T17:18:13Z")

</div>

modpoll 3.7 - FieldTalk™ Modbus® Master Simulator  
Copyright © 2002-2019 proconX Pty Ltd  
Visit [https://www.modbusdriver.com](https://www.modbusdriver.com) for Modbus libraries and tools.

Protocol configuration: MODBUS/TCP  
Slave configuration…: address = 1, start reference = 101, count = 1  
Communication…: plc, port 502, t/o 1.00 s, poll rate 10000 ms  
Data type…: 16-bit register, output (holding) register table

Can’t reach server/slave! Check TCP/IP and firewall settings.

plc is of course the device

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 27, 2020, 5:38pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/44 "2020-04-27T17:38:18Z")

</div>

This sounds like an anti-virus layer. Letting the connection open then buffering the initial real traffic in order to inspect it, and not knowing that it’s holding a complete initial read command packet. Stalling the pipe. Telnet is probably whitelisted by such a layer.

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 5:54pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/45 "2020-04-27T17:54:09Z")

</div>

I don’t see anything running, I see there are ubuntu virus scanners, but none of the processes were it, what else could filter processes like that

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 27, 2020, 5:55pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/46 "2020-04-27T17:55:46Z")

</div>

See if you have anything defined in `LD_PRELOAD`.

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 5:57pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/47 "2020-04-27T17:57:17Z")

</div>

empty envar

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 27, 2020, 5:59pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/48 "2020-04-27T17:59:01Z")

</div>

Sorry, I’m out of ideas. Spin up a new server and test another copy of Ignition in trial mode. Then move the Ignition license if that server works.

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 8:52pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/49 "2020-04-27T20:52:51Z")

</div>

Something I noticed, netstat shows a crap ton of established tcp connections, not sure why these open connections aren’t utilized.

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 9:46pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/50 "2020-04-27T21:46:42Z")

</div>

Okay, so I’m a little further, modpoll does work, for some reason on the ignition server it didn’t like have the url, the ip though worked just fine. So now back to only ignition not requesting data. It seems to keep the tcp connections, they go down from lack of activity, but seem to get reestablished. So what could cause this on an ignition server? thx

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 10:13pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/51 "2020-04-27T22:13:26Z")

</div>

Here’s what I’m getting a lot of:

wireshark:

34 962.392550728 svr → plc TCP 54 [TCP Dup ACK 2#16] [TCP ACKed unseen segment] 48382 → 502 [ACK] Seq=1 Ack=2 Win=28400 Len=0  
35 1022.502767010 plc → svr TCP 54 [TCP Dup ACK 1#17] 502 → 48382 [ACK] Seq=1 Ack=1 Win=2048 Len=0  
36 1022.502806604 svr → plc TCP 54 [TCP Dup ACK 2#17] [TCP ACKed unseen segment] 48382 → 502 [ACK] Seq=1 Ack=2 Win=28400 Len=0  
37 1082.699727026 plc → svr TCP 54 [TCP Dup ACK 1#18] 502 → 48382 [ACK] Seq=1 Ack=1 Win=2048 Len=0  
38 1082.699768172 svr → plc TCP 54 [TCP Dup ACK 2#18] [TCP ACKed unseen segment] 48382 → 502 [ACK] Seq=1 Ack=2 Win=28400 Len=0  
39 1142.898447921 plc → svr TCP 54 [TCP Dup ACK 1#19] 502 → 48382 [ACK] Seq=1 Ack=1 Win=2048 Len=0  
40 1142.898490082 svr → plc TCP 54 [TCP Dup ACK 2#19] [TCP ACKed unseen segment] 48382 → 502 [ACK] Seq=1 Ack=2 Win=28400 Len=0  
41 1203.100141057 plc → svr TCP 54 [TCP Dup ACK 1#20] 502 → 48382 [ACK] Seq=1 Ack=1 Win=2048 Len=0  
42 1203.100168535 svr → plc TCP 54 [TCP Dup ACK 2#20] [TCP ACKed unseen segment] 48382 → 502 [ACK] Seq=1 Ack=2 Win=28400 Len=0

Here’s the only thing in the ignition server logs:

INFO | jvm 1 | 2020/04/27 13:57:55 | ERROR [SocketIODelegate] [13:57:55,875]: [hostname=plc,port=503] Socket connection closed, DriverState was Connected.  
INFO | jvm 1 | 2020/04/27 13:57:56 | ERROR [SocketIODelegate] [13:57:55,868]: [hostname=plc,port=504] Socket connection closed, DriverState was Connected.

The wireshark logs are not aligned in anyway.

Thanks,

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 27, 2020, 11:08pm UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/52 "2020-04-27T23:08:55Z")

</div>

Now we’re getting somewhere the server seems to be stuck in a connecting status for the opc-ua server. So that’s what’s not starting up. What do you guys think?

Thanks

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 28, 2020, 12:05am UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/53 "2020-04-28T00:05:06Z")

</div>

Alright, for all watching this thread finally figured it out. The opc-ua connection was never happening. I had to recreate the connection with the same settings to get it working. So if anyone else sees this check the opc-ua server connection status and deal with that first.

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 28, 2020, 12:05am UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/54 "2020-04-28T00:05:53Z")

</div>

Oh, and thx for everybody’s help, extra eyes never hurt.

---

<div class="post-metadata">

**Author:** ![jpark](https://avatars.discourse-cdn.com/v4/letter/j/a88e57/32.png) [@jpark](https://forum.inductiveautomation.com/u/jpark)\
**Post date:** [April 28, 2020, 12:52am UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/55 "2020-04-28T00:52:59Z")

</div>

Just a quick thought. Did you check to see if the name of the OPC connection is **Ignition OPC-UA Server** vs **Ignition OPC UA Server**?  
Notice the hyphen between OPC and UA

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 28, 2020, 12:56am UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/56 "2020-04-28T00:56:26Z")

</div>

That’s a good troubleshooting tip for an Ignition 8 gateway but this one is 7.8.5 according to OP, so there’s not much reason for that to have happened.

FWIW, we’ve added a warning dialog that pops up when you import tags that reference a non-existent OPC server. Should help this kind of thing.

---

<div class="post-metadata">

**Author:** ![codersmurf](https://avatars.discourse-cdn.com/v4/letter/c/df788c/32.png) [@codersmurf](https://forum.inductiveautomation.com/u/codersmurf)\
**Post date:** [April 28, 2020, 1:05am UTC](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216/57 "2020-04-28T01:05:28Z")

</div>

Yeah, that would have saved some headache. The other comment about the server name, I did have to match the old one before it started working.

Thanks all

[Previous page](https://forum.inductiveautomation.com/t/server-keeps-dropping-modbus-connections-to-all-plcs/34216.md?page=2)