Hi, I have Ignition 7.9 and micro820 PLC with Kepware OPC Server  
I want to show on screen if the PLC has connection so I search a bit of this indication.  
I Browse tags in ignition OPC tag path and show the folders in the picture:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/1/81c5ff6b8f53d5fddebcec60b2918e778717d8bc.png)

which tag I need to choose if I want check PLC communication?  
Thanks.

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [April 26, 2022, 3:40pm UTC](https://forum.inductiveautomation.com/t/show-if-plc-is-connected-micro-820/58854/2 "2022-04-26T15:40:09Z")

</div>

I would imagine Error/NoError.

I usually set up a heatbeat tag in the PLC, then monitor for no change.