# Siemens addressing issue or PLC setting issue?

**URL:** <https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221>\
**Category:** Ignition\
**Created:** [January 4, 2023, 4:01pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221 "2023-01-04T16:01:12Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![AlexZanduR](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/alexzandur/32/31297_2.png) [@AlexZanduR](https://forum.inductiveautomation.com/u/AlexZanduR)\
**Post date:** [January 4, 2023, 4:01pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/1 "2023-01-04T16:01:12Z")

</div>

I was provided these 2 addresses.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/6/c/6ca971ed242dc03127d0f8ef06fe51bc30e06145.png)  
The 1st one worked fine (ns=1;s=[device] **DB10,D54** )  
The 2nd one shows as 'Bad' (ns=1;s=[device] **DB8,X3430.0** )

1st one PLC is S7-300  
2nd one PLC is Simatic ET 200SP (using S7-1500 in Ignition device connection)

After doing some research (not too familiar with siemens) and help from our controls engineer, I came to see the address as Offset 3430 of Data Block 8 with the issue potentially being DInt not Bit, so I tried **DB8,DI3430.0** which failed as well.

I'm suspecting I'm still missing something related to the addressing, though could Ignition connect to the PLC, but not be allowed to pull tags?

Thanks!

---

<div class="post-metadata">

**Author:** ![Sheko29](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sheko29/32/25082_2.png) [@Sheko29](https://forum.inductiveautomation.com/u/Sheko29)\
**Post date:** [January 4, 2023, 4:10pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/2 "2023-01-04T16:10:00Z")

</div>

have you tried using it without the ".0" at the end? just

> (ns=1;s=[device] **DB8,DI3430** )

---

<div class="post-metadata">

**Author:** ![AlexZanduR](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/alexzandur/32/31297_2.png) [@AlexZanduR](https://forum.inductiveautomation.com/u/AlexZanduR)\
**Post date:** [January 4, 2023, 4:13pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/4 "2023-01-04T16:13:26Z")

</div>

yeah, no luck unfortunately

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [January 4, 2023, 4:31pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/5 "2023-01-04T16:31:24Z")

</div>

> [@AlexZanduR](#):
>
> ET 200SP

Is the et200sp acting as remote IO or is it one of the open controllers ?

If its just a remote IO, this connects to a PLC so you have to direct your request to that PLC that controls to the Et200. `ns=1;s=[PLC]DB8,X3430.0` or `ns=1;s=[PLC]DB8,DI3430`

If it is a open controller, do you have any other tags that are working in ignition from that device as there is some settings that need enabled in the hardware config.

Can you grab a screen shot of the DB showing DI3430

---

<div class="post-metadata">

**Author:** ![BRYAN\_MOBLEY](https://avatars.discourse-cdn.com/v4/letter/b/db5fbb/32.png) [@BRYAN\_MOBLEY](https://forum.inductiveautomation.com/u/BRYAN_MOBLEY)\
**Post date:** [January 4, 2023, 9:28pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/6 "2023-01-04T21:28:05Z")

</div>

Yeah the second address you were given is incorrect. Perhaps they meant DB8.DBX343.0? Also is optimized block access unchecked for the DB in the S7-1500?

---

<div class="post-metadata">

**Author:** ![AlexZanduR](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/alexzandur/32/31297_2.png) [@AlexZanduR](https://forum.inductiveautomation.com/u/AlexZanduR)\
**Post date:** [January 4, 2023, 9:29pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/7 "2023-01-04T21:29:52Z")

</div>

Controls engineer informed me he is certain it is NOT a remote IO and provided the below picture.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/0/4/041ce32f0c81e7f529394377dce509490885af24.jpeg)

\*offset 3430.0 is the address he found to the tag I'm needing

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [January 4, 2023, 9:48pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/8 "2023-01-04T21:48:22Z")

</div>

```auto
ns=1;s=[PLC]DB8,DI3430

```

Should work, can you read other values from that PLC? Reason I ask is put/get needs enabled but if you can read other tags then that should already be enabled.

Try read one of the other values like bool value X3466.0

---

<div class="post-metadata">

**Author:** ![AlexZanduR](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/alexzandur/32/31297_2.png) [@AlexZanduR](https://forum.inductiveautomation.com/u/AlexZanduR)\
**Post date:** [January 5, 2023, 1:19pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/9 "2023-01-05T13:19:31Z")

</div>

X3466.0 didn't work. If I go through the Ignition OPC Item Path I can see and assign the same tags for every siemens PLC. Do these count for proof of put/get enabled?  
If not, then that may be the issue.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/f/8f18cfe7a999dff952c045183a00f8349e6137d8.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 5, 2023, 1:45pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/10 "2023-01-05T13:45:10Z")

</div>

> [@AlexZanduR](#):
>
> Do these count for proof of put/get enabled?

No. Those are internally generated by the driver, they don't represent requests on the wire themselves.

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [January 5, 2023, 3:21pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/11 "2023-01-05T15:21:57Z")

</div>

Ask your control engineer to look at the below. Mine is disabled as I dont use the ignition driver, I use the Siemens OPC. But in your case, it needs to be checked.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/0/f02c0261f0bbaff7f9d5ec73e46d1ef216d08de8.png)

---

<div class="post-metadata">

**Author:** ![Sheko29](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sheko29/32/25082_2.png) [@Sheko29](https://forum.inductiveautomation.com/u/Sheko29)\
**Post date:** [January 5, 2023, 3:47pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/12 "2023-01-05T15:47:35Z")

</div>

On siemens PLC Offset is generally hidden until you disable the "optimized block access" option, so maybe it is already disable...

but, check these considerations on your device and try again [Connecting to Siemens S7-1200 and S7-1500 – Inductive Automation Help Center](https://support.inductiveautomation.com/hc/en-us/articles/360047576831-Connecting-to-Siemens-S7-1200-and-S7-1500)

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [January 5, 2023, 3:53pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/13 "2023-01-05T15:53:26Z")

</div>

> [@Sheko29](#):
>
> On siemens PLC Offset is generally disable until you optimize the block access, so maybe it is already enable...

His DB shows the offset column, which is normally hidden if optimized block access is turned on.

---

<div class="post-metadata">

**Author:** ![Sheko29](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sheko29/32/25082_2.png) [@Sheko29](https://forum.inductiveautomation.com/u/Sheko29)\
**Post date:** [January 5, 2023, 3:58pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/14 "2023-01-05T15:58:14Z")

</div>

haha, I said it the other way around, yeah you are right it is hidden until you disable the optimization. (I will correct the previous post to prevent confusion)

---

<div class="post-metadata">

**Author:** ![mjohnson0238](https://avatars.discourse-cdn.com/v4/letter/m/4bbf92/32.png) [@mjohnson0238](https://forum.inductiveautomation.com/u/mjohnson0238)\
**Post date:** [January 9, 2023, 10:28pm UTC](https://forum.inductiveautomation.com/t/siemens-addressing-issue-or-plc-setting-issue/68221/15 "2023-01-09T22:28:47Z")

</div>

Can some one help me figure out where my tag addressing is wrong?

I am using

```auto
ns=1;s=[Doffer M19 North]DB700,X0.2 

```

here is a screenshot of the DB:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/1/114e17b8424c1a1dea624f2a6ebd20e90631ab28.png)

Returning an ERROR for value