# Siemens Enhanced Driver - Arrays for Booleans / DBX

**URL:** <https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788>\
**Category:** Ignition\
**Tags:** siemens\
**Created:** [August 14, 2026, 12:23am UTC](https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788 "2026-08-14T00:23:43Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![kyvski](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kyvski/32/85590_2.png) [@kyvski](https://forum.inductiveautomation.com/u/kyvski)\
**Post date:** [August 14, 2026, 12:23am UTC](https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788/1 "2026-08-14T00:23:44Z")

</div>

According to the docs here:

> **[Siemens Enhanced Driver | Ignition User Manual](https://www.docs.inductiveautomation.com/docs/8.3/ignition-modules/opc-ua/opc-ua-drivers/siemens/siemens-enhanced-driver)**
>
> The AGLink library has been updated to support Siemens S7-1200 G2 PLCs. With this update, the Siemens Enhanced Driver module also now requires a GLIBC version of 2.34 (or newer) on x64 platforms and 2.17 for ARM platforms. This prevents the Siemens...

> "...a variation that resembles the syntax used in the TIA portal, with the addition of supporting arrays"

The format, DB.[DB]X[.BitNumber][ArrayDimensions] is listed  
And an explicit example is given: DB1.DBX8[8] -\> Array of 8 booleans, Bit 0 from offset 8.

Yet, when I try to do this I just get a "Bad\_NodeIdUnknown" error  
Is there a specific setting I have to change to use this?

Sorry if the answer is obvious, I'm not as close to the controls side of things.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 14, 2026, 12:34am UTC](https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788/2 "2026-08-14T00:34:06Z")

</div>

Are you using it in symbolic or absolute addressing mode? and are you sure you have the Siemens Enhanced driver configured and not one of the old ones?

---

<div class="post-metadata">

**Author:** ![kyvski](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kyvski/32/85590_2.png) [@kyvski](https://forum.inductiveautomation.com/u/kyvski)\
**Post date:** [August 14, 2026, 1:35pm UTC](https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788/3 "2026-08-14T13:35:38Z")

</div>

Yes, the device is set to use the enhanced driver. And it's a S7-300, so I'm doing absolute addressing.  
DB1.DBX8[8] just gives me that Bad\_NodeIdUnknown error on the tag.

---

<div class="post-metadata">

**Author:** ![Cody\_Morgan](https://avatars.discourse-cdn.com/v4/letter/c/db5fbb/32.png) [@Cody\_Morgan](https://forum.inductiveautomation.com/u/Cody_Morgan)\
**Post date:** [August 14, 2026, 2:19pm UTC](https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788/4 "2026-08-14T14:19:44Z")

</div>

Unfortunately, this is an error in documentation. The Siemens Enhanced Driver does not support bit arrays when using absolute addressing. I'll reach out to the docs team to get this corrected.

Could you share more about your use case? Feel free to also share this idea on [Ignition Features and Ideas | Inductive Automation](https://ideas.inductiveautomation.com/ignition-features-and-ideas) so that we can better track demand for this feature request.

---

<div class="post-metadata">

**Author:** ![kyvski](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kyvski/32/85590_2.png) [@kyvski](https://forum.inductiveautomation.com/u/kyvski)\
**Post date:** [August 14, 2026, 8:00pm UTC](https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788/5 "2026-08-14T20:00:03Z")

</div>

Ah I see. That was what I was thinking.

For use case - just less tags for each machine, and I so could index them later  
Plus I wasn't sure if it was faster to grab it all at once vs individually  
Not sure how the driver is setup to batch requests

But it was more of just messing around with the driver the first time and seeing behavior that didn't match what the documentation was saying. Separating them per bit shouldn't be an issue.

Thanks for the help!

---

<div class="post-metadata">

**Author:** ![Cody\_Morgan](https://avatars.discourse-cdn.com/v4/letter/c/db5fbb/32.png) [@Cody\_Morgan](https://forum.inductiveautomation.com/u/Cody_Morgan)\
**Post date:** [August 15, 2026, 8:44pm UTC](https://forum.inductiveautomation.com/t/siemens-enhanced-driver-arrays-for-booleans-dbx/116788/6 "2026-08-15T20:44:08Z")

</div>

The driver will batch contiguous bit reads and make a request for however many bytes are necessary. It doesn't do this when writing, so as not to overwrite other bits in the byte.

Alternatively, you can read a byte and mask off the bits yourself via scripting or something, but you're probably better just using one bit per tag. You'd really only want to use an array if the actual PLC data was an array.