Are there any errors in the Ignition logs? Can you upload them?

I suspect you're running into this same issue based on the capture: [Unable to browse tags using Siemens WinCC v 15 - #13 by Kevin.Herron](https://forum.inductiveautomation.com/t/unable-to-browse-tags-using-siemens-wincc-v-15/32605/13)

---