Hi.  
We recently got our ignition connected to the S7-1200 PLC, but any and all tags added to ignition get  
“[CONFIG\_ERROR] null”

PUT/GET is enabled in the plc.  
I have added tags like DB44,X122.0 which is a boolean in DB44, just to test, it gets last value “n/a”, and quality is empty.

How to gain access to the tags, any ideas?

EDIT: Now when i checked wrapper.log i find this:

`INFO | jvm 3 | 2016/07/28 07:21:34 | WARN [CreateMonitoredItemsService] [07:21:34,881]: Returning ServiceFault for request: [CreateMonitoredItemsRequest requestHandle=25814]. StatusCode=StatusCode[Severity=Bad, Subcode=Bad_InternalError]
INFO | jvm 3 | 2016/07/28 07:21:34 | java.lang.NullPointerException
INFO | jvm 3 | 2016/07/28 07:21:34 | WARN [OpcUaConnection$UaSubscriptionChangeListener] [07:21:34,889]: Failed to create 116 items on subscription 'Scanclass 'Default[default]'': UaServiceFaultException: status=Bad_InternalError, message=An internal error occurred as a result of a programming or configuration error.
INFO | jvm 3 | 2016/07/28 07:21:34 | java.util.concurrent.ExecutionException: UaServiceFaultException: status=Bad_InternalError, message=An internal error occurred as a result of a programming or configuration error.`

[attachment=0]tag config errors.png[/attachment]

---

<div class="post-metadata">

**Author:** ![StefanGronberg](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/stefangronberg/32/6288_2.png) [@StefanGronberg](https://forum.inductiveautomation.com/u/StefanGronberg)\
**Post date:** [July 28, 2016, 7:03am UTC](https://forum.inductiveautomation.com/t/siemens-s7-1200-cpu-tags-quality-config-error-now-stale/11976/2 "2016-07-28T07:03:05Z")

</div>

[attachment=0]stale.png[/attachment]Hi.

I checked aroun, and changed the OPC UA Listen IP to the servers IP, to now it went from [CONFIG\_ERROR] to [STALE] instead  
Anyone with any idea how to get the tags to read from a Siemens S7-1500?

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [August 9, 2016, 10:24am UTC](https://forum.inductiveautomation.com/t/siemens-s7-1200-cpu-tags-quality-config-error-now-stale/11976/3 "2016-08-09T10:24:00Z")

</div>

[https://support.inductiveautomation.com/index.php?/Knowledgebase/Article/View/29/2/connecting-to-siemens-s7-1200-and-s7-1500](https://support.inductiveautomation.com/index.php?/Knowledgebase/Article/View/29/2/connecting-to-siemens-s7-1200-and-s7-1500) ❓

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [February 17, 2017, 5:29am UTC](https://forum.inductiveautomation.com/t/siemens-s7-1200-cpu-tags-quality-config-error-now-stale/11976/4 "2017-02-17T05:29:45Z")

</div>

> [@anna](#):
>
> Stefan, DB44,X122.0 is invalid syntax. X is used to address bits, so you should not be specifying the bit after the dot again. Instead, try `DB44,X122`

@anna Sorry anna, but you are wrong. In Siemens PLC you MUST specify bit after the address.  
[device\_name]DB44,X122.0 is correct syntax.

---

<div class="post-metadata">

**Author:** ![anna](https://avatars.discourse-cdn.com/v4/letter/a/779978/32.png) [@anna](https://forum.inductiveautomation.com/u/anna)\
**Post date:** [February 23, 2017, 12:34am UTC](https://forum.inductiveautomation.com/t/siemens-s7-1200-cpu-tags-quality-config-error-now-stale/11976/5 "2017-02-23T00:34:57Z")

</div>

zxcslo, stand corrected 😊 - must have been thinking about something else (like integer offsets)