Hi guys,

I have a s7-1214 hooked up to ignition via the S7-1220 ethernet driver and connected ok.

My issue is getting bits from the memory tags. Eg. M100.1… MX100.1 doesn’t work.

I can see DB tags and DB bits no problem. eg, DB50,X0.0

Has anyone dealt with the TIA portal software and these memory tags?

Cheers for any wisdom… 🙂

Tim…

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [April 22, 2013, 10:09am UTC](https://forum.inductiveautomation.com/t/siemens-s7-1200-tag-issues/6289/2 "2013-04-22T10:09:20Z")

</div>

Just tried it on my Siemens 1500 cpu which works the same as the 1200. Using TIA V12

Here the tag I use [demoplc]MX110.0  
Don’t forget to set it to Boolean.

Craig.

---

<div class="post-metadata">

**Author:** ![0sm0](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/0sm0/32/15228_2.png) [@0sm0](https://forum.inductiveautomation.com/u/0sm0)\
**Post date:** [April 22, 2013, 10:19am UTC](https://forum.inductiveautomation.com/t/siemens-s7-1200-tag-issues/6289/3 "2013-04-22T10:19:53Z")

</div>

Thanks Craig.

I thought I was going crazy. Will give it another go tomorrow.

Cheers for the reply.

Tim…