I've done some testing and everything seems to work as intended. The only issue I ran into was if I try to edit tags in quick succession, only the last one takes. I found this [post](https://forum.inductiveautomation.com/t/writing-to-siemens-tag-structure-via-opc-connection/58217/4) and turned on optimistic writes and allowed data backfill on the tag provider. Thanks!

---