Best advice I've seen on here is from @pturmel:

> [@Typical Performance between Ignition and AB SLC 5/05](http://forum.inductiveautomation.com/t/typical-performance-between-ignition-and-ab-slc-5-05/17262/3):
>
> Check “Comms Servicing Selection” and “MSG Servicing Selection” for channel 1 (S:2/15 & S:33/7). If either is set, it will crush your throughput, as only one request will be processed per scan (Comms) or per certain control flow instructions (MSG).

We don't have any guide. These things are old and slow, so only create tags for the data you need at as slow a rate as you can tolerate. Some people used leased scan classes to speed things up when tags are visible on a screen but disable or slow them down otherwise.

---