# SLOW connection HELP!.. using Allen Bradley NAT 9300 ENA

**URL:** <https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166>\
**Category:** Ignition\
**Created:** [February 4, 2016, 3:54pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166 "2016-02-04T15:54:15Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![BJ\_McClure](https://avatars.discourse-cdn.com/v4/letter/b/df788c/32.png) [@BJ\_McClure](https://forum.inductiveautomation.com/u/BJ_McClure)\
**Post date:** [February 4, 2016, 3:54pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/1 "2016-02-04T15:54:15Z")

</div>

I am having a terrible time getting Ignition to read tags from an AB CompactLogix L33er when going through an Allen Bradley NAT translator 9300-ENA… the NAT appears to be setup correctly and speed tests by our IT department show it at full duplex, sends and received huge packets very well… I added the L33er PLC device to Ignition and it shows okay but in the designer I can’t see tag values and when running the project display fields are red with no data updates… at this point, I am completely stumped. We have no problem with Ignition on other devices that are connected directly to our network …just this one trying to go thru the NAT…

The only thing I can figure is the L33er PLC Device is ver 21.11 and the Ignition driver shows ver 20 or later…

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 4, 2016, 4:15pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/2 "2016-02-04T16:15:23Z")

</div>

[quote=“BJ McClure”]The only thing I can figure is the L33er PLC Device is ver 21.11 and the Ignition driver shows ver 20 or later…[/quote]Actually, it shows “v20 or prior”. That driver won’t work. You must use the new Logix driver.

---

<div class="post-metadata">

**Author:** ![BJ\_McClure](https://avatars.discourse-cdn.com/v4/letter/b/df788c/32.png) [@BJ\_McClure](https://forum.inductiveautomation.com/u/BJ_McClure)\
**Post date:** [February 4, 2016, 9:22pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/3 "2016-02-04T21:22:43Z")

</div>

Where can I get the new driver?..

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 4, 2016, 9:38pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/4 "2016-02-04T21:38:23Z")

</div>

What version of Ignition are you on? It’s included in 7.7 and later, and should show up as “Allen-Bradley Logix Driver” in the driver list.

---

<div class="post-metadata">

**Author:** ![BJ\_McClure](https://avatars.discourse-cdn.com/v4/letter/b/df788c/32.png) [@BJ\_McClure](https://forum.inductiveautomation.com/u/BJ_McClure)\
**Post date:** [February 5, 2016, 1:52pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/5 "2016-02-05T13:52:15Z")

</div>

running ver 7.7.1

In the OPC-UA, adding devices only shows firmware ver 20 and prior processors… My processor is ver 21.11

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 5, 2016, 3:16pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/6 "2016-02-05T15:16:18Z")

</div>

[quote=“BJ McClure”]running ver 7.7.1

In the OPC-UA, adding devices only shows firmware ver 20 and prior processors… My processor is ver 21.11[/quote]You must have deleted the module that has the new driver. It should look like this:[attachment=0]LogixDriverV21.png[/attachment]  
You need [this module](https://s3.amazonaws.com/files.inductiveautomation.com/release/build7.7.1/2014092209/Logix%20Driver-module.modl) for v7.7.1.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 5, 2016, 4:01pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/7 "2016-02-05T16:01:19Z")

</div>

I would recommend upgrading to 7.7.6 while you’re at it…

---

<div class="post-metadata">

**Author:** ![BJ\_McClure](https://avatars.discourse-cdn.com/v4/letter/b/df788c/32.png) [@BJ\_McClure](https://forum.inductiveautomation.com/u/BJ_McClure)\
**Post date:** [February 12, 2016, 6:54pm UTC](https://forum.inductiveautomation.com/t/slow-connection-help-using-allen-bradley-nat-9300-ena/11166/8 "2016-02-12T18:54:17Z")

</div>

Upgraded to 7.8

Problem solved…Thanks for the help!