# \[SOLVED\] Connecting Studio 5000 Emulator to Ignition

**URL:** <https://forum.inductiveautomation.com/t/solved-connecting-studio-5000-emulator-to-ignition/31380>\
**Category:** Ignition\
**Created:** [January 17, 2020, 7:23pm UTC](https://forum.inductiveautomation.com/t/solved-connecting-studio-5000-emulator-to-ignition/31380 "2020-01-17T19:23:08Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![bmeyers](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bmeyers/32/37453_2.png) [@bmeyers](https://forum.inductiveautomation.com/u/bmeyers)\
**Post date:** [January 17, 2020, 7:23pm UTC](https://forum.inductiveautomation.com/t/solved-connecting-studio-5000-emulator-to-ignition/31380/1 "2020-01-17T19:23:08Z")

</div>

Has anyone successfully in the last month connected their Ignition to a version of Studio 5000 Emulator? If so, what version of Ignition, Studio 5000 Emulator, RSLinx, and OS are you running? Did you install the OPC Core Components Redistributable package x86 or x64?

I am running Windows7 Enterprise 64-bit, Ignition 8.0.7, Studio 5000 Emulator v30.01.00, and RSLinx 3.9. In my Ignition I can see the PLC tags on the emulator but the values never come through.

Yes, I’ve successfully setup SoftLogix but Rockwell only supports up to version 23.

---

<div class="post-metadata">

**Author:** ![Paullys50](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paullys50/32/3324_2.png) [@Paullys50](https://forum.inductiveautomation.com/u/Paullys50)\
**Post date:** [January 20, 2020, 1:44am UTC](https://forum.inductiveautomation.com/t/solved-connecting-studio-5000-emulator-to-ignition/31380/2 "2020-01-20T01:44:31Z")

</div>

Earlier this year I was successful with Emulate v32, 8.0.2/3. Can’t recall x86/x64 fo OPC core components but was able to create an OPC topic in RS Linx and connect it to the OPC-com module.

Pretty sure I just followed this: [https://support.inductiveautomation.com/index.php?/Knowledgebase/Article/View/4/0/setting-up-and-troubleshooting-opc-com-connections](https://support.inductiveautomation.com/index.php?/Knowledgebase/Article/View/4/0/setting-up-and-troubleshooting-opc-com-connections)

It did not like large projects, once I had 20,000+ tags it would take 5+ minutes for emulate values to appear in Ignition tags.

---

<div class="post-metadata">

**Author:** ![bmeyers](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bmeyers/32/37453_2.png) [@bmeyers](https://forum.inductiveautomation.com/u/bmeyers)\
**Post date:** [January 20, 2020, 3:18am UTC](https://forum.inductiveautomation.com/t/solved-connecting-studio-5000-emulator-to-ignition/31380/3 "2020-01-20T03:18:11Z")

</div>

Thank you so much. With a combination of your link and the following:

> [@OPC-DA to RSLinx Classic (Emulated PLC)](http://forum.inductiveautomation.com/t/opc-da-to-rslinx-classic-emulated-plc/11667):
>
> While doing testing I found a way to use the OPC-DA connection to create a link between 2 computers and read values from an RSLinx topic I had created to an emulated PLC. Note: Because this uses OPC-DA (because RSLinx does not yet support OPC-UA), this will only work on Windows (unless an OPC-DA client has been released for the linux version since last I used Ignition) Pre-requisites: Two computers (or VMs) that can communicate to each other using IP addresses and computer names. A computer …

I was able to get my Emulator setup working on Windows 7 Enterprise 64 bit,opc-core-components-redistributables-3.00.107-20180130 installed, Ignition 7.9.10, Studio 23, and Emulator 23.

Tomorrow I'll try a similar setup on Studio 30 and Emulator 30.