# Some tag disconnects when connecting a different device with different modbus device ID

**URL:** <https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941>\
**Category:** Ignition\
**Tags:** ignition83\
**Created:** [June 11, 2026, 12:43am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941 "2026-06-11T00:43:06Z")\
**Posts on this page:** 12\
**Page:** 2

<div class="post-metadata">

**Author:** ![bschroeder](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bschroeder/32/13260_2.png) [@bschroeder](https://forum.inductiveautomation.com/u/bschroeder)\
**Post date:** [June 14, 2026, 11:22am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/21 "2026-06-14T11:22:16Z")

</div>

You can find better but you won't pay more.

---

<div class="post-metadata">

**Author:** ![brillian.teope](https://avatars.discourse-cdn.com/v4/letter/b/22d042/32.png) [@brillian.teope](https://forum.inductiveautomation.com/u/brillian.teope)\
**Post date:** [July 10, 2026, 12:43am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/22 "2026-07-10T00:43:27Z")

</div>

Hello lane.duncan,

Could you help me out to figure out what is going on with the tags keep on dropping intermittently? I tried the tip you provided but still the problem persists.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/a/fa48ac989f9418f6f1dfa2a1cd8be81d1782feb3.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/0/4/04600c63e71d12dbf9553685ce0a9154ee005b7f.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/6/d6660bbcda79be3e26f8134c51d06774c54f3be4.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/a/7a976d6819609891551516f95a501ac2a73c70dc.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/6/a62ea94ae59eba8237fd141601f94799c05e3bd1.jpeg)

[ZWGW01\_02 LoRa Modbus Transceiver Datasheet.pdf](https://forum.inductiveautomation.com/uploads/short-url/ky5ynAmYzWO1Ceh52UeYjDOospT.pdf) (1.5 MB)

Here is the datasheet for your reference

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/9/b9ecd9d1a81654a0e880b52d1c0e70357bf25df5.png)

here is the port settings of the ZWGW01 Gateway

---

<div class="post-metadata">

**Author:** ![lane.duncan](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lane.duncan/32/83700_2.png) [@lane.duncan](https://forum.inductiveautomation.com/u/lane.duncan)\
**Post date:** [July 10, 2026, 6:50am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/23 "2026-07-10T06:50:40Z")

</div>

The connection to PWR MTR02 is gone. There are many locations in this system where the connection can go bad. You need to narrow down which one of the 5 connections shown (one blue, two green, two red) is causing the issue.

Are the two inverters associated with that power meter dropping out at the same time?

Are both power meters dropping out at the same time?

Are all six devices dropping out at the same time?

I am also curious about TCP max sockets = 2 with the KICK option. Could the device be kicking Ignition offline due to detecting too many connections?

Perhaps adding “Device Offline” alarms for all six devices might help troubleshoot the issue.

Edit: That frequency reading is quite low. Are you sure you are not having power issues in the field?

---

<div class="post-metadata">

**Author:** ![brillian.teope](https://avatars.discourse-cdn.com/v4/letter/b/22d042/32.png) [@brillian.teope](https://forum.inductiveautomation.com/u/brillian.teope)\
**Post date:** [July 10, 2026, 2:36pm UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/24 "2026-07-10T14:36:36Z")

</div>

Hello Lane,

I missed out on putting a 120 ohm terminating resistor in the inverter 2 terminals, I will observe tomorrow if that solves the issue. I reviewed the manual and learned that it has an internal 120ohm that will activate when shorting the B-R and B- terminals on the Zwgw02, if that is enabled, there should be a 120ohm resistor tapped on the farthest device, in this case the inverter 2.

---

<div class="post-metadata">

**Author:** ![brillian.teope](https://avatars.discourse-cdn.com/v4/letter/b/22d042/32.png) [@brillian.teope](https://forum.inductiveautomation.com/u/brillian.teope)\
**Post date:** [July 10, 2026, 2:43pm UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/25 "2026-07-10T14:43:04Z")

</div>

I suppose that causes reflection during the data transmission on the rs485 wires.

---

<div class="post-metadata">

**Author:** ![brillian.teope](https://avatars.discourse-cdn.com/v4/letter/b/22d042/32.png) [@brillian.teope](https://forum.inductiveautomation.com/u/brillian.teope)\
**Post date:** [July 10, 2026, 2:44pm UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/26 "2026-07-10T14:44:27Z")

</div>

Are the two inverters associated with that power meter dropping out at the same time?

Yes they are all on the same bus

---

<div class="post-metadata">

**Author:** ![brillian.teope](https://avatars.discourse-cdn.com/v4/letter/b/22d042/32.png) [@brillian.teope](https://forum.inductiveautomation.com/u/brillian.teope)\
**Post date:** [July 10, 2026, 2:45pm UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/27 "2026-07-10T14:45:27Z")

</div>

Are all six devices dropping out at the same time?

They drop randomly on each device

---

<div class="post-metadata">

**Author:** ![lane.duncan](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lane.duncan/32/83700_2.png) [@lane.duncan](https://forum.inductiveautomation.com/u/lane.duncan)\
**Post date:** [July 11, 2026, 5:33am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/28 "2026-07-11T05:33:34Z")

</div>

Repeating this:

> My experience with low cost devices is that bad tag quality happens quite frequently. These devices tend to be powered by chipmunks on treadmills, which overheat and take frequent breaks. Bad quality tags are to be expected from time to time. This is the trade off for the low cost.

And this:

> Perhaps adding “Device Offline” alarms for all six devices might help troubleshoot the issue.

If those Inverters have any kind of detailed status information I would also configure detailed alarms for those.

---

<div class="post-metadata">

**Author:** ![brillian.teope](https://avatars.discourse-cdn.com/v4/letter/b/22d042/32.png) [@brillian.teope](https://forum.inductiveautomation.com/u/brillian.teope)\
**Post date:** [July 11, 2026, 5:53am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/29 "2026-07-11T05:53:14Z")

</div>

Adding 120ohms solves the issue, however another issue comes along when I add 1 based Addressing device, how can we have mixed (zero based and 1 based) without having drop outs?

---

<div class="post-metadata">

**Author:** ![brillian.teope](https://avatars.discourse-cdn.com/v4/letter/b/22d042/32.png) [@brillian.teope](https://forum.inductiveautomation.com/u/brillian.teope)\
**Post date:** [July 11, 2026, 5:54am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/30 "2026-07-11T05:54:38Z")

</div>

Previously both power meters and inverters are zero based. Should I just decrement the 1 based device by 1?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 11, 2026, 6:48pm UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/31 "2026-07-11T18:48:20Z")

</div>

> [@brillian.teope](#):
>
> Should I just decrement the 1 based device by 1?

I would say yes, always. The protocol on the wire is always zero-based. One-based addressing is a convenient crutch to deal with ambiguity. (My alternate driver doesn't support one-based addressing at all.)

---

<div class="post-metadata">

**Author:** ![nminchin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nminchin/32/6911_2.png) [@nminchin](https://forum.inductiveautomation.com/u/nminchin)\
**Post date:** [July 13, 2026, 12:40am UTC](https://forum.inductiveautomation.com/t/some-tag-disconnects-when-connecting-a-different-device-with-different-modbus-device-id/115941/32 "2026-07-13T00:40:14Z")

</div>

> [@David\_Stone](#):
>
> see you've never compared an AB unmanaged switch to the rest of the market

It doesn't apply like this for scada systems either.... The more you pay, the less you get, and the more antiquated the code base (and far more frustrating a development experience!)