Hi everybody,

I'm fighting with some string tags.  
I try to create to tags for two strings from a PLC. I can find these strings in my PLC at the same datablock. The first string is at the offset of 0.0 (length = 25) and the second string is at 28.0 (length = 16).  
If I try to configure the first tag as a string with the OPC path : [PLC name] DB1,String0 everything works fine and I recieve the string content.

If I delete this tag and create a new one for the second string with the OPC path: [PLC name],String28 I recieve the also the correct string content.

So far so good.  
The problem occurs when I try to use both tags at the same time. Then I recieve "Bad" as value and all values from the PLC are written in red.

I also tried to give the string tags a length: for example: [PLC name]String0.25  
But the issue is still there when I implement to string tags at the same time.

Has anybody an idea how to solve this problem?

Regards  
Inken

---

<div class="post-metadata">

**Author:** ![taglias](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@taglias](https://forum.inductiveautomation.com/u/taglias)\
**Post date:** [January 16, 2023, 7:27am UTC](https://forum.inductiveautomation.com/t/string-array-tag/68618/2 "2023-01-16T07:27:34Z")

</div>

Hello Inken,  
try declaring just two tags:  
[PLCname]DB1,STRING0.25  
[PLCname]DB1,STRING28.16

This should work.  
I don't know the string length used by the driver if you leave it empty, I suppose 210 (the max length, as written in the manual, probably; keep in mind that the default length in the PLC, if you don't declare one in the DB, is 254, per Siemens S7 manual).