Hello Team,  
We have requirement to integrate Thermotron 8800 display with Ignition. Thermotron 8800 display support TCP/IP. We want to know feasibility of Integration Ignition with Thermotron 8800 display with TCP driver.  
If yes, Can you confirm how would be tag access I mean it can be browse automatically or need to create manually.

Thanks in advance for support.

Regards,  
Dhiraj Pawar

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [October 3, 2023, 11:19am UTC](https://forum.inductiveautomation.com/t/support-for-integration-ignition-with-thermotron-8800-display-with-ignition/79963/2 "2023-10-03T11:19:31Z")

</div>

A quick look through their manual suggests that you will have to build your own.

You may want to contact Thermtron, though, as they may have ottions not yet listed on the website.

> **[Contact Us | Thermotron Industries](https://thermotron.com/contact-us/)**
>
> World Headquarters 291 Kollen Park Drive Holland, MI 49423 USA 800-409-3449 (toll-free, sales & marketing) 800-272-2589 (toll-free, parts, service & technical support) 616-393-4580 (local, sales & marketing) 616-392-5643 (fax)

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [October 3, 2023, 7:02pm UTC](https://forum.inductiveautomation.com/t/support-for-integration-ignition-with-thermotron-8800-display-with-ignition/79963/3 "2023-10-03T19:02:44Z")

</div>

Did you look at the C# TCP "drivers" here?  
[https://thermotron.com/service-2/instrument-drivers/](https://thermotron.com/service-2/instrument-drivers/)

Looks like they're just sending ASCII commands and getting responses.

---

<div class="post-metadata">

**Author:** ![dhiraj.pawar](https://avatars.discourse-cdn.com/v4/letter/d/3ec8ea/32.png) [@dhiraj.pawar](https://forum.inductiveautomation.com/u/dhiraj.pawar)\
**Post date:** [October 4, 2023, 7:40am UTC](https://forum.inductiveautomation.com/t/support-for-integration-ignition-with-thermotron-8800-display-with-ignition/79963/4 "2023-10-04T07:40:45Z")

</div>

Hello ,  
I believe that If the device supports TCP/IP communication, then the TCP driver should be able to communicate with it. The TCP driver listen directly t port and collects data sent to that port.

@michael.flagler So we need to do programming to send ASCII command & get response or It can be browse automatically with configuration in Ignition TCP driver?

@michael.flagler@JordanCClark Please help me for That

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [October 4, 2023, 11:46am UTC](https://forum.inductiveautomation.com/t/support-for-integration-ignition-with-thermotron-8800-display-with-ignition/79963/5 "2023-10-04T11:46:44Z")

</div>

> [@dhiraj.pawar](#):
>
> So we need to do programming to send ASCII command & get response

Yes.

> [@dhiraj.pawar](#):
>
> It can be browse automatically with configuration in Ignition TCP driver?

No, the TCP driver will not automatically do this for you. It has no idea of what it is connecting to. One write tag, one read tag.

I would say your best options are as follows:

- Script your communications. Send request, read response, write to tag.
- Contact Thermotron and see if there is an OPC package available.