Morning

I have a Kepware OPC server running as a OPC-DA COM connection I have now set it up as an OPC-UA connection.

I naively thought I would just rename the new connection as the old connection and all would be well.  
It seems that OPC path has some additional characters (ns=2:s=)as a prefix, is there a simple way to globally implement this or is it a manual job?

Chris

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 8, 2013, 2:45pm UTC](https://forum.inductiveautomation.com/t/swapping-opc-servers/5832/2 "2013-02-08T14:45:51Z")

</div>

You can export your SQLTags, do a find/replace to add the prefix, then import them again.

Make sure to do a gateway backup before you go messing around with your tags though. ![:thumb_left:](https://us1.discourse-cdn.com/inductiveautomation/original/1X/e26afb081ddde6df016df6ee49159cf56aaca688.gif ":thumb\_left:")