# Tag from plc not coming out on opc server

**URL:** <https://forum.inductiveautomation.com/t/tag-from-plc-not-coming-out-on-opc-server/26211>\
**Category:** Ignition\
**Created:** [July 2, 2019, 12:05am UTC](https://forum.inductiveautomation.com/t/tag-from-plc-not-coming-out-on-opc-server/26211 "2019-07-02T00:05:35Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![alex.cordova.ee](https://avatars.discourse-cdn.com/v4/letter/a/f1d935/32.png) [@alex.cordova.ee](https://forum.inductiveautomation.com/u/alex.cordova.ee)\
**Post date:** [July 2, 2019, 12:05am UTC](https://forum.inductiveautomation.com/t/tag-from-plc-not-coming-out-on-opc-server/26211/1 "2019-07-02T00:05:35Z")

</div>

I created OPC tags that already existed in PLC. Then I made a new PLC tag in the PLC and it does not come out. I tried several new tags and none of them come out. I have been doing this for months and never had this issue. PLC tag is active and running in PLC

---

<div class="post-metadata">

**Author:** ![witman](https://avatars.discourse-cdn.com/v4/letter/w/d2c977/32.png) [@witman](https://forum.inductiveautomation.com/u/witman)\
**Post date:** [July 2, 2019, 1:21am UTC](https://forum.inductiveautomation.com/t/tag-from-plc-not-coming-out-on-opc-server/26211/2 "2019-07-02T01:21:05Z")

</div>

Assuming you’re using a Logix driver, try going to Config-\>OPC-UA-\>Devices on the Ignition gateway web page and then tap More-\>Refresh Browse (if available) next to the PLC device. Otherwise, tap Edit next to PLC device, and then Save on the following page.

---

<div class="post-metadata">

**Author:** ![alex.cordova.ee](https://avatars.discourse-cdn.com/v4/letter/a/f1d935/32.png) [@alex.cordova.ee](https://forum.inductiveautomation.com/u/alex.cordova.ee)\
**Post date:** [July 2, 2019, 8:14pm UTC](https://forum.inductiveautomation.com/t/tag-from-plc-not-coming-out-on-opc-server/26211/3 "2019-07-02T20:14:24Z")

</div>

Got it and worked thank you.