Probably not, due to the nature of the protocols involved your fastest is probably going to be ~250ms. Pturmel's [Ethernet IP Communication Suite](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/172) driver is known to be faster (users routinely have 100ms poll rates) but I'm not sure that could reach this poll rate either.

If this is for logging to a database, collect the values at your faster rate and stuff them into a buffer array on the device, and read chunks of the array at a set slower rate.

IE, have 5 seconds worth of data storage space, filling into it at your 16.67ms rate. Read the latest 1s of data into ignition and write it to a DB table. Read the next 1s of data and repeat. And keep repeating that process.

This is the normal approach for recording high speed data on a slower polling protocol.

---

_[View the full topic](https://forum.inductiveautomation.com/t/tag-group-scan-rate/97800)._