# Tag Groups for every tag?

**URL:** <https://forum.inductiveautomation.com/t/tag-groups-for-every-tag/88089>\
**Category:** Ignition\
**Created:** [March 29, 2024, 8:51pm UTC](https://forum.inductiveautomation.com/t/tag-groups-for-every-tag/88089 "2024-03-29T20:51:17Z")\
**Posts on this page:** 1\
**Showing post:** 2

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 29, 2024, 11:55pm UTC](https://forum.inductiveautomation.com/t/tag-groups-for-every-tag/88089/2 "2024-03-29T23:55:23Z")

</div>

If the many tag groups have the same pace, then it doesn't matter. If different paces, it could matter.

But is sounds like the classis AOI problem with Ignition's native driver. Some topics to review:

> [@Cannot read some tags inside Rockwell AOI](https://forum.inductiveautomation.com/t/cannot-read-some-tags-inside-rockwell-aoi/38393/3):
>
> What Mike said, but also: Don't. All AOI's have EnableIn and EnableOut booleans that are locked to "Hidden" and therefore prevent most optimization of the data traffic to read instances of these data types. Ignition's Logix driver cannot do bulk reads on AOIs. Do very much of this and your Logix driver will choke. I strongly recommend that any AOI you design yourself use one or more InOut parameters of another data type, with instances of those datatypes elsewhere. Place all of your extern…

> [@Ignition & Logix Best Practice Tips for better communications](https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386/6):
>
> I've had success with the legacy ControlLogix doing so. Was helpful with an Omron NJ processor more recently. If you are referring to the bombshell in this topic, then yes: If you are going to be changing things in the PLC, you might also consider switching your fastest tag group (or part of it) to "Class 1" Ethernet/IP. This module was created to deal with large numbers of tags at a 100ms pace: { /Shameless plug. }

> [@Ignition & Logix Best Practice Tips for better communications](https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386/19):
>
> Relief for those who don't want to break up their AOIs is now available:

---

_[View the full topic](https://forum.inductiveautomation.com/t/tag-groups-for-every-tag/88089)._