Hi there, what kind of rate do you suggest for e.g. control buttons (e.g. run motor) and real time indications?  
Is less than 1000ms too fast (e.g. 500ms 250ms)?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 25, 2021, 1:59am UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/2 "2021-03-25T01:59:08Z")

</div>

I recommend 100ms. Unfortunately, to get that kind of seamless UI performance, you usually cannot use a normal OPC driver. I am a bit biased, but your question was the spur for the existence of my Ethernet/IP module:

> [@Snappy user interfaces with the Ethernet/IP Module](http://forum.inductiveautomation.com/t/snappy-user-interfaces-with-the-ethernet-ip-module/12617):
>
> Automation Professionals [Ethernet/IP Class1 Communications Module](https://www.automation-pros.com/modulesales.html) has been in beta for a few months with no recent issues. A release to production use is approaching soon and I thought I’d share a test project and its matching PLC code I’ve been using to exercise the module’s base features. In the simplest setup, this driver presents a virtual I/O chassis to to the outside world, populated with up to 100 virtual I/O modules – I/O modules that also appear to be ControlLogix processors with user…

---

<div class="post-metadata">

**Author:** ![Yfactor](https://avatars.discourse-cdn.com/v4/letter/y/e79b87/32.png) [@Yfactor](https://forum.inductiveautomation.com/u/Yfactor)\
**Post date:** [March 25, 2021, 2:00am UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/3 "2021-03-25T02:00:33Z")

</div>

@pturmel sorry you mean 100ms or 1000ms?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 25, 2021, 2:06am UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/4 "2021-03-25T02:06:17Z")

</div>

One hundred milliseconds. One-tenth of a second. That is the performance boundary where human operators are more likely to think a button is “instant” than not. Real pushbuttons wired to real PLC remote I/O typically have latencies in the tens of milliseconds or less. You have to get close to that to “feel” like a real button.

---

<div class="post-metadata">

**Author:** ![Yfactor](https://avatars.discourse-cdn.com/v4/letter/y/e79b87/32.png) [@Yfactor](https://forum.inductiveautomation.com/u/Yfactor)\
**Post date:** [March 25, 2021, 2:20am UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/5 "2021-03-25T02:20:47Z")

</div>

😂 Sorry I just had to make sure I got it right. wow so with that module that you’ve suggested, we can set the rate to 100ms wow  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/9/39fce6699e149a28b4ccb4f858b1fe8336bb1513.png)  
so would 1000ms be a kind of a recommended rate for standard Ignition OPC?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 25, 2021, 2:27am UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/6 "2021-03-25T02:27:14Z")

</div>

> [@Yfactor](#):
>
> so would 1000ms be a kind of a recommended rate for standard Ignition OPC?

It's a good place to start, which is why it's the default.

You can go faster but it depends on the device and how many tags you're asking for at that rate.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 25, 2021, 11:15am UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/7 "2021-03-25T11:15:00Z")

</div>

> [@Yfactor](#):
>
> set the rate to 100ms wow

Yes, for data in Class 1 Ethernet/IP packets (I/O slave, I/O master, or Producer/Consumer tags). But you wouldn't use the Leased/Driven rate, but the main Rate. (Leased doesn't make sense for a continuous flow of UDP packets.) You would set it to match the RPI in the connection.

---

<div class="post-metadata">

**Author:** ![Yfactor](https://avatars.discourse-cdn.com/v4/letter/y/e79b87/32.png) [@Yfactor](https://forum.inductiveautomation.com/u/Yfactor)\
**Post date:** [March 25, 2021, 8:52pm UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/8 "2021-03-25T20:52:39Z")

</div>

Hi Kevin, thank you the reason I asked is because I wanted to make sure my understanding is correct with this. (i think I’ve asked something similar before on other forum)  
I have total Request Count of 68  
1st scenario (all on 1000ms)

 ![all 1000ms](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/e/7eefc117b4ea97ddb042d6caf7bc9475d1ea10f6.png)  
2nd (some on 300 ms and 1000ms)  
 ![all 300ms](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/6/5632283f8a5196e7f3d9fa6ba1358ae9e3de5ba5.png)

I have my machine stop start control button on the fast update group that I swap between 1000 and 300.

so performance wise are my tags responding faster when it is in 300ms or 1000ms?

Cheers

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 25, 2021, 9:23pm UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/9 "2021-03-25T21:23:38Z")

</div>

They should be responding faster when using 300ms.

---

<div class="post-metadata">

**Author:** ![Yfactor](https://avatars.discourse-cdn.com/v4/letter/y/e79b87/32.png) [@Yfactor](https://forum.inductiveautomation.com/u/Yfactor)\
**Post date:** [March 25, 2021, 11:38pm UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/10 "2021-03-25T23:38:28Z")

</div>

Hi Kevin but its Mean Response time is faster on 1000ms when we have 1000 and 300 ms (6.91ms) ? but the mean Response time is faster on both when compared to everything on 1000ms

---

<div class="post-metadata">

**Author:** ![dtompkins](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@dtompkins](https://forum.inductiveautomation.com/u/dtompkins)\
**Post date:** [May 4, 2021, 12:00am UTC](https://forum.inductiveautomation.com/t/tag-subscription-rates/44885/11 "2021-05-04T00:00:45Z")

</div>

Correct me if I am wrong, but wouldn’t you also improve responsiveness by spreading the reads across scan classes? Even if they trigger at the same frequency?