> [@nminchin](#):
>
> Keep your tag value change scripts extremely fast

This. Events on tags themselves should run in single digit milliseconds or less, due to the likelihood of blocking the system-wide thread pool for tags. That means **no database operations** nor any **network access operations** nor any **recursive searches** in these events.

Gateway tag change events in a project have their own (unbounded) queues and their own threads. Put any time-consuming operations there. But do note that only one thread services all the tags for a given event, so there can be more latency.

---