# Transaction Standard stop record

**URL:** <https://forum.inductiveautomation.com/t/transaction-standard-stop-record/14354>\
**Category:** Ignition\
**Tags:** ignition79\
**Created:** [May 19, 2017, 2:20pm UTC](https://forum.inductiveautomation.com/t/transaction-standard-stop-record/14354 "2017-05-19T14:20:04Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![edo](https://avatars.discourse-cdn.com/v4/letter/e/e5b9ba/32.png) [@edo](https://forum.inductiveautomation.com/u/edo)\
**Post date:** [May 19, 2017, 2:20pm UTC](https://forum.inductiveautomation.com/t/transaction-standard-stop-record/14354/1 "2017-05-19T14:20:04Z")

</div>

I have a problem in standard transaction for recording the setup of machine.  
I record it when one value of tags change.  
I see the problem when I switch off and switch on the machine(server opc connection) because the transaction record double time the equal value.  
Is there a system to avoid it?

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [May 19, 2017, 5:26pm UTC](https://forum.inductiveautomation.com/t/transaction-standard-stop-record/14354/2 "2017-05-19T17:26:40Z")

</div>

Sounds like this should be covered by the ‘Prevent trigger caused by group start’ setting:

 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/f/f25d5226db2447750354ff2517bd71d2b4af3402.png)

---

<div class="post-metadata">

**Author:** ![edo](https://avatars.discourse-cdn.com/v4/letter/e/e5b9ba/32.png) [@edo](https://forum.inductiveautomation.com/u/edo)\
**Post date:** [May 22, 2017, 9:01am UTC](https://forum.inductiveautomation.com/t/transaction-standard-stop-record/14354/3 "2017-05-22T09:01:58Z")

</div>

> [@paul-griffith](#):
>
> Sounds like this should be covered by the 'Prevent trigger caused by group start' setting:

Ah ok but this option is possible to active when I tick "Execute this Group on a trigger" and after I decide to use one tag.  
Is it not possible with all tags?

How can I use trigger in the best mode?