I’ve been evaluating Ignition on my laptop and every time I change wireless networks the connection to the UA Server is broken and never comes back. The only way that I have found to fix it so far is to uninstall and reinstall Ignition, is there something I am doing wrong?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 22, 2011, 3:47am UTC](https://forum.inductiveautomation.com/t/ua-server-connection-broken/3203/2 "2011-08-22T03:47:58Z")

</div>

You’re probably going to have issues because your IP address is changing when you change networks. Under “OPC-UA \> Settings” on the Ignition gateway there is a setting called Endpoint Address. Next time you change networks go set this to the IP address you receive and then restart the UA module.

---

<div class="post-metadata">

**Author:** ![Micky.Franks](https://avatars.discourse-cdn.com/v4/letter/m/c57346/32.png) [@Micky.Franks](https://forum.inductiveautomation.com/u/Micky.Franks)\
**Post date:** [August 22, 2011, 3:00pm UTC](https://forum.inductiveautomation.com/t/ua-server-connection-broken/3203/3 "2011-08-22T15:00:22Z")

</div>

That fixed it. I was changing the endpoint address, but I had never restarted the UA module.