Looks like you are not the first to have this question, looks like it can be fixed with formatting.

> [@UDT Parameter math is not evaluating correctly](https://forum.inductiveautomation.com/t/udt-parameter-math-is-not-evaluating-correctly/47911):
>
> This does not work. Note that the Description worked. [image] Actual OPC path for the alarm: ns=1;s=[PL\_STACKER]PL\_Stacker.Alarm[0].2 Parameters. The alarm configuration with the parameter math. [image] Testing… [image] [image] Both failed… The non math reference obviously works fine. [image] Am I doing this wrong? The documentation seems pretty clear. Any suggestions?

Just tried it out, it works, you were close:

```auto
{BaseAddress/2|#}

```

---