# Unable to browse tags using Siemens WinCC v 15

**URL:** <https://forum.inductiveautomation.com/t/unable-to-browse-tags-using-siemens-wincc-v-15/32605>\
**Category:** Ignition\
**Created:** [February 25, 2020, 9:52pm UTC](https://forum.inductiveautomation.com/t/unable-to-browse-tags-using-siemens-wincc-v-15/32605 "2020-02-25T21:52:48Z")\
**Posts on this page:** 1\
**Showing post:** 9

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 18, 2020, 10:02pm UTC](https://forum.inductiveautomation.com/t/unable-to-browse-tags-using-siemens-wincc-v-15/32605/9 "2020-05-18T22:02:55Z")

</div>

@eduardogarcia after looking at your Wireshark you may need to set the Max Per Operation advanced setting on the connection to something very low, like 50 or 100 to start, and try again. It seems the server is not exposing the nodes that indicate its operation limits.

---

_[View the full topic](https://forum.inductiveautomation.com/t/unable-to-browse-tags-using-siemens-wincc-v-15/32605)._