# Upgrading Versions

**URL:** <https://forum.inductiveautomation.com/t/upgrading-versions/1836>\
**Category:** Ignition\
**Created:** [May 11, 2010, 1:24pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836 "2010-05-11T13:24:03Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![DennisWomack](https://avatars.discourse-cdn.com/v4/letter/d/51bf81/32.png) [@DennisWomack](https://forum.inductiveautomation.com/u/DennisWomack)\
**Post date:** [May 11, 2010, 1:24pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836/1 "2010-05-11T13:24:03Z")

</div>

I am missing something.

I was running the demo version of 7.09 and upgraded to 7.1 and now the opc tags are not being scanned.

I backed up the project before trying to upgrade.

I upgraded by just executing the Windows installer for 7.1.

The web server is running. The context is running. The devices say they are connected.

What am I doing wrong?

Thanks for the help.

Dennis

---

<div class="post-metadata">

**Author:** ![Travis.Cox](https://avatars.discourse-cdn.com/v4/letter/t/b9bd4f/32.png) [@Travis.Cox](https://forum.inductiveautomation.com/u/Travis.Cox)\
**Post date:** [May 11, 2010, 4:52pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836/2 "2010-05-11T16:52:13Z")

</div>

Dennis, please give us a call at (800) 266-7798 so we can take the problem. We need more information to figure out why the tags are not updating.

---

<div class="post-metadata">

**Author:** ![DennisWomack](https://avatars.discourse-cdn.com/v4/letter/d/51bf81/32.png) [@DennisWomack](https://forum.inductiveautomation.com/u/DennisWomack)\
**Post date:** [May 11, 2010, 6:32pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836/3 "2010-05-11T18:32:23Z")

</div>

It will be a while. I am tied up on something else.

Earlier upgrades seemed to go without a hitch. The last couple of times I had issues.

Talk to you later.

Dennis

---

<div class="post-metadata">

**Author:** ![Travis.Cox](https://avatars.discourse-cdn.com/v4/letter/t/b9bd4f/32.png) [@Travis.Cox](https://forum.inductiveautomation.com/u/Travis.Cox)\
**Post date:** [May 11, 2010, 8:27pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836/4 "2010-05-11T20:27:57Z")

</div>

What are the versions of each module in Ignition? You can find these in the gateway config section under Configuration -\> Modules.

---

<div class="post-metadata">

**Author:** ![DennisWomack](https://avatars.discourse-cdn.com/v4/letter/d/51bf81/32.png) [@DennisWomack](https://forum.inductiveautomation.com/u/DennisWomack)\
**Post date:** [May 11, 2010, 9:39pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836/5 "2010-05-11T21:39:11Z")

</div>

The OPCUA Server says that it is faulted:

java.lang.Exception: Error during ActivateSession: Bad\_UserAccessDenied  
com.inductiveautomation.xopc.client.ua.ActivateSession.activateSession(ActivateSession.java:162)  
com.inductiveautomation.xopc.client.ua.UAClient.connect(UAClient.java:95)  
com.inductiveautomation.xopc.client.sropc.OPCUAServer.connect(OPCUAServer.java:394)  
com.inductiveautomation.xopc.client.sropc.OPCUAServer.verifyConnectionState(OPCUAServer.java:417)  
com.inductiveautomation.ignition.gateway.opc.OPCManagerImpl$ServerWrapper.verifyConnectionState(OPCManagerImpl.java:663)  
com.inductiveautomation.ignition.gateway.opc.OPCManagerImpl$OPCConnectionKeepalive.run(OPCManagerImpl.java:550)  
com.inductiveautomation.ignition.common.execution.impl.BasicExecutionEngine$TrackedTask.run(BasicExecutionEngine.java:450)  
java.util.concurrent.Executors$RunnableAdapter.call(Unknown Source)  
java.util.concurrent.FutureTask$Sync.innerRunAndReset(Unknown Source)  
java.util.concurrent.FutureTask.runAndReset(Unknown Source)  
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.access$101(Unknown Source)  
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.runPeriodic(Unknown Source)  
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(Unknown Source)  
java.util.concurrent.ThreadPoolExecutor$Worker.runTask(Unknown Source)  
java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source)  
java.lang.Thread.run(Unknown Source)  
Subscriptions

OPC-UA Drivers is 1.09  
I’ll swap that out and see if that fixes it.

Dennis

---

<div class="post-metadata">

**Author:** ![DennisWomack](https://avatars.discourse-cdn.com/v4/letter/d/51bf81/32.png) [@DennisWomack](https://forum.inductiveautomation.com/u/DennisWomack)\
**Post date:** [May 12, 2010, 2:37pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836/6 "2010-05-12T14:37:46Z")

</div>

I uninstalled and then reinstalled 7.1.

No errors showed with new naked installation.

I restored a backup taken in the backup/restore section and now there is an error with the opcua connections.

IgnitionOPCUA is faulted. It says Error during ActivateSession:Bad\_UserAccessDenied

details:  
com.inductiveautomation.xopc.common.UAException: null  
com.inductiveautomation.xopc.common.stack.TCPChannel.sendAsynchronous(TCPChannel.java:314)  
com.inductiveautomation.xopc.common.stack.TCPChannel.send(TCPChannel.java:295)  
com.inductiveautomation.xopc.common.stack.TCPChannel.getEndpoints(TCPChannel.java:163)  
com.inductiveautomation.xopc.common.stack.TCPChannel.getEndpoints(TCPChannel.java:149)  
com.inductiveautomation.xopc.client.sropc.OPCUAServer.getEndpoint(OPCUAServer.java:436)  
com.inductiveautomation.xopc.client.sropc.OPCUAServer.connect(OPCUAServer.java:377)  
com.inductiveautomation.xopc.client.sropc.OPCUAServer.verifyConnectionState(OPCUAServer.java:417)  
com.inductiveautomation.ignition.gateway.opc.OPCManagerImpl$ServerWrapper.verifyConnectionState(OPCManagerImpl.java:663)  
com.inductiveautomation.ignition.gateway.opc.OPCManagerImpl$OPCConnectionKeepalive.run(OPCManagerImpl.java:550)  
com.inductiveautomation.ignition.common.execution.impl.BasicExecutionEngine$TrackedTask.run(BasicExecutionEngine.java:450)  
java.util.concurrent.Executors$RunnableAdapter.call(Unknown Source)  
java.util.concurrent.FutureTask$Sync.innerRunAndReset(Unknown Source)  
java.util.concurrent.FutureTask.runAndReset(Unknown Source)  
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.access$101(Unknown Source)  
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.runPeriodic(Unknown Source)  
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(Unknown Source)  
java.util.concurrent.ThreadPoolExecutor$Worker.runTask(Unknown Source)  
java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source)  
java.lang.Thread.run(Unknown Source)  
Subscriptions  
default.0 @1000ms enable live values  
Address Last Value Quality Timestamp  
[IgnitionOPCUA][504WrapperRMplcA]Global.HMI\_LastScanTime null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][504WrapperRMplcA]Global.HMI\_MaxScanTime null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][504WrapperRMplcA]Global.MCM1\_ScanTime null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_CIP\_CONTROL]Global.BATTER\_HOLD\_TANK\_HOMOG\_DIVERT\_1\_V412.is\_Closed null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_CIP\_CONTROL]Global.BATTER\_HOLD\_TANK\_HOMOG\_DIVERT\_1\_V412.is\_Open null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_CIP\_CONTROL]Global.BATTER\_HOLD\_TANK\_HOMOG\_DIVERT\_2\_V413.is\_Closed null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_CIP\_CONTROL]Global.BATTER\_HOLD\_TANK\_HOMOG\_DIVERT\_2\_V413.is\_Open null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_DEPOSITOR]Global.Auto null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_DEPOSITOR]Global.WorkData.Name.STRING null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_DOUGH\_HOMOG]B3:2 null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_INJECTOR]Global.Auto null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_INJECTOR]Global.WorkData.Name.STRING null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[0] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[1] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[2] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[3] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[4] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[5] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[6] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[7] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[8] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Carriers\_Visible\_at\_DEPOSITOR.Carriers\_Visible\_at\_DEPOSITOR[9] null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Drive\_on\_indicator null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Trays\_per\_minute null Bad\_NoDataAvailable 2010-05-12 09:41:42  
[IgnitionOPCUA][L504\_OVEN]Global.Wonderware\_Recipe\_Name.STRING null Bad\_NoDataAvailable 2010-05-12 09:41:42  
\<\< \< 1 2 \> \>\> Total subscribed items: 30

default.1 @10000ms enable live values  
Address Last Value Quality Timestamp  
\<\< \< \> \>\> Total subscribed items: 0

Another place says:  
Error getting endpoint response from url “opc.tcp://localhost:4096/iaopcua”

Could this be caused by Windows Firewall?

Thanks for the help.

Dennis

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 12, 2010, 7:01pm UTC](https://forum.inductiveautomation.com/t/upgrading-versions/1836/7 "2010-05-12T19:01:18Z")

</div>

It looks like your username and password are setup wrong. I have a couple things for you to check:

1. In the module status area of the gateway ([localhost:8088/main/web/status/modules](http://localhost:8088/main/web/status/modules)) can you check the version number of all your modules and post those here?

2. In the OPC-UA settings area ([localhost:8088/main/web/config/xopc.settings](http://localhost:8088/main/web/config/xopc.settings)) what authentication profile is set? It should be “opcua-module” with allowed roles “ReadWrite”.

Then in the security \> authentication area ([localhost:8088/main/web/config/security.auth](http://localhost:8088/main/web/config/security.auth)) you should have a “opcua-module” profile. This profile should have a user called “opcuauser”.

The default password is “password”. In your connection to the OPC-UA server ([localhost:8088/main/web/config/opc.connections](http://localhost:8088/main/web/config/opc.connections)) you should have the previous username and password specified.

This is all done by default but I suspect by restoring an older gateway backup things are getting a little jumbled.