# UserTokenPolicy

**URL:** <https://forum.inductiveautomation.com/t/usertokenpolicy/25575>\
**Category:** Ignition\
**Created:** [June 5, 2019, 1:04pm UTC](https://forum.inductiveautomation.com/t/usertokenpolicy/25575 "2019-06-05T13:04:11Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![athayer](https://avatars.discourse-cdn.com/v4/letter/a/eb8c5e/32.png) [@athayer](https://forum.inductiveautomation.com/u/athayer)\
**Post date:** [June 5, 2019, 1:04pm UTC](https://forum.inductiveautomation.com/t/usertokenpolicy/25575/1 "2019-06-05T13:04:11Z")

</div>

I’m using Ignition 7.6 with Kepware 6.6.  
This is to allow a legacy application to communicate with AB PLCs v21 and higher.  
The Kepware itself is all set and communicates with both a AB5500 PLC and an AB5069 PLC.  
When I create the OPC-UA server connection I get this error;  
’ no acceptable UserTokenPolicy present on selected endpoint’

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 5, 2019, 2:43pm UTC](https://forum.inductiveautomation.com/t/usertokenpolicy/25575/2 "2019-06-05T14:43:19Z")

</div>

This means you’re either connecting without a username and password but KSE requires one, or you’re connecting _with_ a username and password but KSE is not configured to accept that.

It’s more likely the former, and you need to configure a username and password.