# Version: 8.1.3 (b2021030309) No alarm message in "alarm status table"

**URL:** <https://forum.inductiveautomation.com/t/version-8-1-3-b2021030309-no-alarm-message-in-alarm-status-table/44473>\
**Category:** Ignition Early Access\
**Created:** [March 15, 2021, 3:22pm UTC](https://forum.inductiveautomation.com/t/version-8-1-3-b2021030309-no-alarm-message-in-alarm-status-table/44473 "2021-03-15T15:22:51Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![jaap.de.cloe](https://avatars.discourse-cdn.com/v4/letter/j/c77e96/32.png) [@jaap.de.cloe](https://forum.inductiveautomation.com/u/jaap.de.cloe)\
**Post date:** [March 15, 2021, 3:22pm UTC](https://forum.inductiveautomation.com/t/version-8-1-3-b2021030309-no-alarm-message-in-alarm-status-table/44473/1 "2021-03-15T15:22:51Z")

</div>

I want a message in the “alarm status table” when an integer goes above a setpoint. When I configure an alarm and I set the [alarm mode settings] on above setpoint f.e. = 5 and the [any change] on true.  
When the tag value goes above 5, the alarm is only recorded in the “alarm journal table” but not in the “alarm status table”

When I set [any change] on false the alarm message will be showed in the “alarm status table”

I want to set the [any change] condition on true because I want to execute a [alarm active] script every time the setpoint value changes above the setpoint