**Author:** ![diego.marques](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/diego.marques/32/79285_2.png) [@diego.marques](https://forum.inductiveautomation.com/u/diego.marques)\
**Post date:** [August 25, 2025, 5:24pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/1 "2025-08-25T17:24:53Z")

</div>

Hi, I’m new to this forum. I’m trying to bind my parameters `{Inst_Name}` and `{Inst_Table}` using a named query chart to pass my udt tag values; Although it is working during runtime, when I open my template, I got a cyclic error popup in my parameter. My Named Query “Query\_Inst“ is very simple:

`Select`  
`t_stamp,`  
`{Inst_Name}`  
`From {Inst_Table}`

Inst\_Name and Inst\_Table are my column and table names of type QueryString in SQL Server; When I bind my UDT Tags in the value field in the chart - {INST\_PT\_Projeção\_P.Dados::CONF.TAG} for Inst\_Name and - {INST\_PT\_Projeção\_P.Dados::CONF.Hist} for Inst\_Table I get this error:

`java.lang.Exception: Error running query:com.inductiveautomation.factorypmi.application.gateway.NQuery@16b700a4@6000msOn: INST_PT_Projeção_P.INST_PT_Projeção_P.Chart.Dataat com.inductiveautomation.factorypmi.application.gateway.QueryManager$QueryExecutor.run(QueryManager.java:311)at java.base/java.lang.Thread.run(Unknown Source)Caused by: com.inductiveautomation.ignition.client.gateway_interface.GatewayException: java.lang.Exception: Missing value for query parameter {Inst_Name}`

any help would be greatly appreciated!

---

<div class="post-metadata">

**Author:** ![ryan.white](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryan.white/32/73193_2.png) [@ryan.white](https://forum.inductiveautomation.com/u/ryan.white)\
**Post date:** [August 25, 2025, 5:32pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/2 "2025-08-25T17:32:36Z")

</div>

~~In simplest terms, cyclic binding error/warning means you have some how bound something to itself, either directly or through a chain of bindings.~~ We'll need to see how your template/table is actually set up to be able to help further.

Show a picture (or multiple) of your table setup and the binding configurations on the table/template.

> [@diego.marques](#):
>
> `java.lang.Exception: Missing value for query parameter {Inst_Name}`

Based on this error it seems you aren't passing a value to one of the query parameters. Double check your binding configuration. The cyclic binding error might be causing the value to not be passed.

Also, edit your post to have the stack trace as preformatted text, see [Wiki - how to post code on this forum](https://forum.inductiveautomation.com/t/wiki-how-to-post-code-on-this-forum/77831). You can edit your post by clicking the pencil icon in the bottom right.

Edit: Misunderstood the cyclic error

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [August 25, 2025, 5:49pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/3 "2025-08-25T17:49:19Z")

</div>

Ensure that the parameters match **exactly** - same case, no leading/trailing spaces, that you've saved in the designer since making changes, etc.

---

<div class="post-metadata">

**Author:** ![diego.marques](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/diego.marques/32/79285_2.png) [@diego.marques](https://forum.inductiveautomation.com/u/diego.marques)\
**Post date:** [August 25, 2025, 5:55pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/4 "2025-08-25T17:55:49Z")

</div>

@**[paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith),**  
The error only occurs in edition mode when I open my template. In runtime my chart works ok. I took these prints to ilustrate how I built my template and the SQL query:

 ![UDT_Tag](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/c/ec923bf8d4313ff27c664e30c5ed477296d2cdbd.png)

 ![NamedQuery](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/f/5f7a60a725c0b3298dd7bd6731317e9579c3e1ab.png)

 ![Template](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/7/f7e6eece51812978d57aa90aebaddb5ff7b7f27b.png)

---

<div class="post-metadata">

**Author:** ![ryan.white](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryan.white/32/73193_2.png) [@ryan.white](https://forum.inductiveautomation.com/u/ryan.white)\
**Post date:** [August 25, 2025, 6:02pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/5 "2025-08-25T18:02:52Z")

</div>

Can you also show your template's parameter setup/config? Cyclic error is something that should not be happening, full stop.

Also, on the query binding dialog, select the value box for each parameter and press enter. I've seen where just clicking outside of the box does not apply the expression.

Completely different (but related) topic, based on your query, each device has a separate DB table in the database, correct? Is there a reason why you don't have a single tall table with a column for `value`, `deviceId` and `timestamp`? That would allow you to filter on just the device ID, and maybe timespan, instead of using query strings in a named query. It also allows you to add/remove devices without having to deal with adding or removing tables.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [August 25, 2025, 6:06pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/6 "2025-08-25T18:06:20Z")

</div>

I would hazard a guess that it's a combination of UDT type parameters and query string parameters in your named query. You should contact our support department to make an official bug report: [https://support.inductiveautomation.com/hc/en-us](https://support.inductiveautomation.com/hc/en-us)

---

<div class="post-metadata">

**Author:** ![diego.marques](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/diego.marques/32/79285_2.png) [@diego.marques](https://forum.inductiveautomation.com/u/diego.marques)\
**Post date:** [August 25, 2025, 6:21pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/7 "2025-08-25T18:21:29Z")

</div>

> [@ryan.white](#):
>
> Also, on the query binding dialog, select the value box for each parameter and press enter. I've seen where just clicking outside of the box does not apply the expression.

I tried that, unsuccessfully…

> [@ryan.white](#):
>
> Can you also show your template's parameter setup/config? Cyclic error is something that should not be happening, full stop.

 ![TemplateParameters](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/e/decf3469bbec61816e70c8954bdd5405f5cf309e.png)

---

<div class="post-metadata">

**Author:** ![ryan.white](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryan.white/32/73193_2.png) [@ryan.white](https://forum.inductiveautomation.com/u/ryan.white)\
**Post date:** [August 25, 2025, 6:30pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/8 "2025-08-25T18:30:12Z")

</div>

> [@diego.marques](#):
>
> I got a cyclic error popup

Let me try to clarify on my end, as I realize I might be misunderstanding something. When you say cyclic error popup do you mean:  
A) The popup shows an error with something along the lines of `circular reference` or similar?  
B) The popup keeps reappearing at a set rate with the same error, which is the error that you posted?

I would advise _against_ using UDT parameters, and instead pass the tag path to the UDT instance you want to target/use as a string to your template. From there, bind template custom properties indirectly to necessary UDT members, using the tag path passed to build the full path.

You can find plenty of posts on the forums on why using UDT parameters on views/templates is not recommended.

---

<div class="post-metadata">

**Author:** ![diego.marques](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/diego.marques/32/79285_2.png) [@diego.marques](https://forum.inductiveautomation.com/u/diego.marques)\
**Post date:** [August 25, 2025, 7:12pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/9 "2025-08-25T19:12:38Z")

</div>

> [@ryan.white](#):
>
> do you mean:  
> A) The popup shows an error with something along the lines of `circular reference` or similar?  
> B) The popup keeps reappearing at a set rate with the same error, which is the error that you posted?

B → Once I configure my NamedQuery parameter value inside my template chart as `{INST_PT_Projeção_P.Dados::CONF.TAG}` for `{Inst_Name}` and - `{INST_PT_Projeção_P.Dados::CONF.Hist`} for `{Inst_Table}`, the error popup keeps reappearing at a set rate.

`{INST_PT_Projeção_P.Dados::CONF.TAG}` and `{INST_PT_Projeção_P.Dados::CONF.Hist}` are the paths built by the “Insert Property“ button, ![Insert_Property](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/6/560d035d7d013c94e539b2abb2891c171e4f5641.png) pointing to my template custom parameter “Dados“ in wich we found `.CONF.TAG` and `.CONF.Hist` members, from my UDT.

 ![UDT_Properties](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/a/7a153f24160a2822b1a437ef9d6c9c78a75d3c99.png)

---

<div class="post-metadata">

**Author:** ![ryan.white](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryan.white/32/73193_2.png) [@ryan.white](https://forum.inductiveautomation.com/u/ryan.white)\
**Post date:** [August 25, 2025, 7:18pm UTC](https://forum.inductiveautomation.com/t/vision-chart-named-query-parameter-inside-a-template-for-udt-tag/110152/10 "2025-08-25T19:18:10Z")

</div>

> [@diego.marques](#):
>
> error popup keeps reappearing at a set rate.

Okay, that it is from the query attempting to re-execute at whatever rate and having that error each execution. I originally thought you were getting an error regarding a circular reference.