Hello all. Does anyone know if there is a limit to the number of Vision Client Launcher windows for projects on an **Ignition Edge** gateway? A client reported having trouble opening a third window.

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 24, 2026, 10:36pm UTC](https://forum.inductiveautomation.com/t/vision-client-limit-on-ignition-edge/114155/2 "2026-02-24T22:36:38Z")

</div>

Yes, it’s two maximum, and one MUST run on the gateway. With Edge Perspective, you can run two max remote from the gateway.

If you need more, standard Ignition is the only option.

---

<div class="post-metadata">

**Author:** ![chukwuemeka.agu](https://avatars.discourse-cdn.com/v4/letter/c/bb73d2/32.png) [@chukwuemeka.agu](https://forum.inductiveautomation.com/u/chukwuemeka.agu)\
**Post date:** [February 25, 2026, 2:29pm UTC](https://forum.inductiveautomation.com/t/vision-client-limit-on-ignition-edge/114155/3 "2026-02-25T14:29:50Z")

</div>

I see, thank you

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 26, 2026, 4:34pm UTC](https://forum.inductiveautomation.com/t/vision-client-limit-on-ignition-edge/114155/4 "2026-02-26T16:34:00Z")

</div>

Forum tip: if you don’t require further advice on this matter you can click “solution” =)