# Wago 750-841 PLC via Modbus to Ignition

**URL:** <https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888>\
**Category:** Archived Topics\
**Created:** [April 22, 2011, 2:09am UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888 "2011-04-22T02:09:04Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![marcboyd](https://avatars.discourse-cdn.com/v4/letter/m/ea5d25/32.png) [@marcboyd](https://forum.inductiveautomation.com/u/marcboyd)\
**Post date:** [April 22, 2011, 2:09am UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888/1 "2011-04-22T02:09:04Z")

</div>

Has anyone been able to successfully connect to a Wago 750-841 using the Modbus driver in Ignition? I configured it and it says it’s connected, but i don’t see any tags. My PLC is currently communicating with an ifix Scada using an iFix MBE driver. This is a Modbus Ethernet driver. Any suggestions?

Thanks!

Marc

---

<div class="post-metadata">

**Author:** ![AlThePal](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/althepal/32/3603_2.png) [@AlThePal](https://forum.inductiveautomation.com/u/AlThePal)\
**Post date:** [April 22, 2011, 10:44am UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888/2 "2011-04-22T10:44:23Z")

</div>

What tags are you expecting to see? Nothing will be generated automatically - you will have to directly address the required registers by setting the OPC Item Path in a SQLTag e.g. [Device1]HR10 to read holding register number 10 (Modbus address 40010) from Device1.

Look at the User Manual under Gateway Configuration/OPC/Ignition OPC-UA Server/Drivers/Modbus Drivers/Modbus Ethernet/Addressing for more information.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 22, 2011, 3:10pm UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888/3 "2011-04-22T15:10:46Z")

</div>

You can also configure address mappings by following the [addresses] link next to the device you have configured.

---

<div class="post-metadata">

**Author:** ![gnguyen](https://avatars.discourse-cdn.com/v4/letter/g/41988e/32.png) [@gnguyen](https://forum.inductiveautomation.com/u/gnguyen)\
**Post date:** [April 25, 2011, 8:49am UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888/4 "2011-04-25T08:49:46Z")

</div>

Hello Marc,

You can have a quick setup video [http://www.youtube.com/watch?v=DStcOXnAdo4](http://www.youtube.com/watch?v=DStcOXnAdo4).

Hope this can help

---

<div class="post-metadata">

**Author:** ![ch4plus](https://avatars.discourse-cdn.com/v4/letter/c/439d5e/32.png) [@ch4plus](https://forum.inductiveautomation.com/u/ch4plus)\
**Post date:** [April 25, 2011, 11:50am UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888/5 "2011-04-25T11:50:26Z")

</div>

Hello Marc,

if you have connect the modbus-driver from Ignition to the Wago-PLC insert 5 variables to the Wago PLC:

[color=#0040FF]VAR\_GLOBAL[/color]  
var1 [color=#0040FF]AT [/color][color=#FF4000]%MW1000[/color] : [color=#0000FF]WORD;[/color] (_Modbus-Adress 13288_)  
var2 [color=#0040FF]AT [/color][color=#FF4000]%MW1001[/color] : [color=#0000FF]WORD;[/color] (_Modbus-Adress 13289_)  
var3 [color=#0040FF]AT [/color][color=#FF4000]%MW1002[/color] : [color=#0000FF]WORD;[/color] (_Modbus-Adress 13290_)  
var4 [color=#0040FF]AT [/color][color=#FF4000]%MW1003[/color] : [color=#0000FF]WORD;[/color] (_Modbus-Adress 13291_)  
var5 [color=#0040FF]AT [/color][color=#FF4000]%MW1004[/color] : [color=#0000FF]WORD;[/color] (_Modbus-Adress 13292_)  
[color=#0040FF]END\_VAR[/color]

Upload the program to the Wago-PLC and start it.

Go to your Ignition-Modbus-Driver and click adresses, add a new row like this:  
Prefix = test  
Start = 0  
End = 4  
Step = false  
Unit ID = 1  
Modbus Type = HoldingRegister(Int16)  
ModbusAdress = 13288  
Radix = 10

Save it, open the Ignition Designer, add a new OPC-Tag from the OPC-UA Modbus-Device and check it.  
If it don’t work correct, please check the modbus-device-driver, advanced-categories:  
Use Zero Base Addressing = false  
Reverse Numeric Word Order = false  
Reverse String Byte Order = false  
Right Justify Strings = false.

ch4plus

---

<div class="post-metadata">

**Author:** ![marcboyd](https://avatars.discourse-cdn.com/v4/letter/m/ea5d25/32.png) [@marcboyd](https://forum.inductiveautomation.com/u/marcboyd)\
**Post date:** [April 25, 2011, 6:42pm UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888/6 "2011-04-25T18:42:19Z")

</div>

Thanks for all of the help guys! I was finally able to read data from the Wago. Now I have another question. I need to read in some string values from the PLC, but they are just coming in as a number.

I have the tag setup in the designer with a path as:  
[RoomController] HRS12376:20  
According to the user manual this should read modbus address 12376 at a length of 20.

I must be missing something, but I can’t see it. Any suggestions would be greatly appreciated!!

Thanks In Advance,

Marc

---

<div class="post-metadata">

**Author:** ![ch4plus](https://avatars.discourse-cdn.com/v4/letter/c/439d5e/32.png) [@ch4plus](https://forum.inductiveautomation.com/u/ch4plus)\
**Post date:** [May 2, 2011, 4:22pm UTC](https://forum.inductiveautomation.com/t/wago-750-841-plc-via-modbus-to-ignition/2888/7 "2011-05-02T16:22:57Z")

</div>

Your example: [RoomController] HRS12376:20

Wago PLC:

VAR\_GLOBAL  
test\_string [color=#0040FF]AT [/color][color=#BF40FF]%MW88[/color] : [color=#0040FF]STRING(20)[/color]; (_Modbus-Adress 12376_)  
END\_VAR

Ignition OPC-UA Modbus-Device:  
Reverse String Byte Order = true

Tag setup in the designer:  
Datatype=string  
[RoomController] HRS12376:20

This should be work.

Gruessle  
ch4plus