<div class="post-metadata">

**Author:** ![kgamble](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kgamble/32/8019_2.png) [@kgamble](https://forum.inductiveautomation.com/u/kgamble)\
**Post date:** [March 31, 2025, 3:08pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/61 "2025-03-31T15:08:59Z")

</div>

> [@Ryan\_Deardorff](#):
>
> What are the `projectPaths` relative to?

They should be relative to the position of the saved VS Code workspace.

So if you do "Save Workspace As" in VS Code, wherever you choose to put that file (We typically do it in the root) of the repo, then it would be relative to that.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/b/8bf07b359158c984c0f0f972af9af83b55baf588.png)

Typically we are using this extension with gateways running in docker containers, and not on direct windows installs, so arguably I have not ran through that specific scenario before.

You could try creating a VS Code Workspace in your `C:\Program Files\Inductive Automation\Ignition\data` directory, and then setting the paths to just be `projects`?

Or you could try making the workspace in your home directory for your user, and then putting in a full hardcoded projectPath for `C:\Program Files\Inductive Automation\Ignition\data\projects`? Here is a proposed workspace file for that setup. If you make a folder (wherever you typically use as a working directory, lets pretends its `C:\Users\username\ignition`

With the file at `C:\Users\username\ignition\ignition.code-workspace.json`

```json
{
	"folders": [
    {
      "name": "Root", # Reference to C:\Users\username\ignition
      "path": "."
    },
    {
      "name": "Projects Directory",
      "path": "C:\Program Files\Inductive Automation\Ignition\data\projects"
    }
  ],
	"settings": {
    "ignitionFlint.ignitionGateways": [
      {
        "label": "Ignition",
        "address": "http://localhost:8088",
        "projectPaths": [
          "C:\Program Files\Inductive Automation\Ignition\data\projects"
        ],
        "updateDesignerOnSave": true,
        "forceUpdateDesigner": true,
        "supportsProjectScanEndpoint": true
      }
    ]
	}
}

```

Caveat, that I dont have access to a windows computer at the moment and so I did not test that at all.

---

<div class="post-metadata">

**Author:** ![chandler](https://avatars.discourse-cdn.com/v4/letter/c/e9a140/32.png) [@chandler](https://forum.inductiveautomation.com/u/chandler)\
**Post date:** [April 24, 2025, 4:12pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/62 "2025-04-24T16:12:33Z")

</div>

Would it ever be possible to allow other JVM languages as the scripting language? It would be nice to write scripts directly in Java or Kotlin.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 24, 2025, 4:59pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/63 "2025-04-24T16:59:40Z")

</div>

Technically it may be; Kotlin at one point had support for the now defunct JSR-223 scripting engine thing.

Whether we would actually pursue that is another thing.

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [April 24, 2025, 6:00pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/64 "2025-04-24T18:00:32Z")

</div>

Could be a designer feature tbh - Visual Studio lets you type cw then tab to auto type `console.writeLine()`. Would be huge for `system.perspective.print()`.

---

<div class="post-metadata">

**Author:** ![Ryan\_Deardorff](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryan_deardorff/32/63815_2.png) [@Ryan\_Deardorff](https://forum.inductiveautomation.com/u/Ryan_Deardorff)\
**Post date:** [April 24, 2025, 6:16pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/65 "2025-04-24T18:16:37Z")

</div>

> [@jacob\_geers](#):
>
> Would be huge for `system.perspective.print()`

I use AutoHotKey for that, as well as my Ignition login/pwd. Together they have undoubtedly saved me hours worth of time over just the last couple years.

---

<div class="post-metadata">

**Author:** ![brownd18](https://avatars.discourse-cdn.com/v4/letter/b/4af34b/32.png) [@brownd18](https://forum.inductiveautomation.com/u/brownd18)\
**Post date:** [April 30, 2025, 5:44pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/66 "2025-04-30T17:44:13Z")

</div>

When you are using VScode for Project Scripting edits, how do you get VScode to recognize system or other local scripting functions.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/b/fbe267a89bb33295f04b5cc80a6e5b1c46d516e6.png)  
Notifications is another Scripting folder within the project.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [April 30, 2025, 6:12pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/67 "2025-04-30T18:12:01Z")

</div>

@thecesrom.git has a set of Python "stubs" that you can import to a modern Python editor corresponding to the system functions:

> **[GitHub - ignition-devs/ignition-api-8.1: 📦 Package for the Ignition Scripting API version...](https://github.com/ignition-devs/ignition-api-8.1)**
>
> 📦 Package for the Ignition Scripting API version 8.1

> [@thecesrom/Ignition repo has moved to ignition-api GitHub org](https://forum.inductiveautomation.com/t/thecesrom-ignition-repo-has-moved-to-ignition-api-github-org/57278):
>
> What started as a personal project I uploaded to [GitHub back in January 2018](https://forum.inductiveautomation.com/t/ignition-mock-scripts-on-github/16468), a few months passed and the repo [found a new home](https://forum.inductiveautomation.com/t/new-github-repo-and-new-python-package/17962). Two years later it grew [branches](https://forum.inductiveautomation.com/t/ignition-repo-now-with-branches/37932), and later it became a [Python Package](https://forum.inductiveautomation.com/t/ignition-scripting-api-now-available-via-pypi/50800). And this week the project reached a new milestone gaining 1,000 downloads in a month. rocket Now, onto announcements. First, I’d like to thank all who have cloned, forked, and installed the package, and second, I’d like to announce that (hopefully) the project has moved to its final home unde…

You will probably still have to manually `import system` _in your editor_ to convince it things are in scope. You don't want `import system` to end up in your final script, though it's not really catastrophic if it does.

---

<div class="post-metadata">

**Author:** ![brownd18](https://avatars.discourse-cdn.com/v4/letter/b/4af34b/32.png) [@brownd18](https://forum.inductiveautomation.com/u/brownd18)\
**Post date:** [April 30, 2025, 8:20pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/68 "2025-04-30T20:20:45Z")

</div>

Why don't you want import system to end up in the final script?

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [April 30, 2025, 8:30pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/69 "2025-04-30T20:30:59Z")

</div>

From `import system` many people end up with `import MyProjectLibraryScript`, which _does_ cause problems \[1\] \[2\].

It's also unnecessary and can lead to "cargo culting", where people just assume they have to `import system` for system functions to work, which is not true anywhere \[3\].

* * *

1. 

> [@\[IGN-6503\]Project Library Script Initialization Races](https://forum.inductiveautomation.com/t/ign-6503-project-library-script-initialization-races/98636):
>
> Are you annoyed by pseudo-random breakage in Ignition project library scripting? Odd top-level constants being garbled, or operations in the top level that have side effects running twice? Or more? Not happening much, but always around project edits, and sometimes even on gateway restart? Yeah, me too. frowning_face Poking around under the hood back in the spring, for a module development task, I ran across some problematic IA bytecode and pinged some people. But it went nowhere, as I co…

2. 

> [@\[IGN-4437\] Ignition occasionally forgets how Python works?](https://forum.inductiveautomation.com/t/ign-4437-ignition-occasionally-forgets-how-python-works/69635/21):
>
> If you cannot do my option 4, consider this option 5, superior to option 3: c = Constants system.db.runNamedQuery(c.GET\_PATH, {c.XYZ\_ID\_COLUMN\_NAME:variable}) The fundamental issue is that Ignition is extremely multi-threaded, including for the jython interpreters. Note the "s" on interpreters. Some multi-threading issues that cannot occur in CPython, due to its single interpreter lifetime, absolutely can occur with jython in Ignition. A piece of your code that triggers the lookup of Constan…

3. except in gateway scoped event scripts, until 8.3.0 is released

---

<div class="post-metadata">

**Author:** ![ben.hutche](https://avatars.discourse-cdn.com/v4/letter/b/9fc348/32.png) [@ben.hutche](https://forum.inductiveautomation.com/u/ben.hutche)\
**Post date:** [June 14, 2025, 2:44am UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/70 "2025-06-14T02:44:04Z")

</div>

This is probably a code snippet, you can add your own in vscode.

You could also use  
import system.perspective.print as log  
To shorten it a bit as well.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 14, 2025, 2:12pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/71 "2025-06-14T14:12:44Z")

</div>

> [@ben.hutche](#):
>
> import system.perspective.print as log

Be aware that `import` always takes the interpreter's modules lock, which can stall your script if something big is importing elsewhere (highly parallel as noted above). All use of `import` should be in project library scripts at the outermost level, never inside function definitions, or performance will suffer.

---

<div class="post-metadata">

**Author:** ![ben.hutche](https://avatars.discourse-cdn.com/v4/letter/b/9fc348/32.png) [@ben.hutche](https://forum.inductiveautomation.com/u/ben.hutche)\
**Post date:** [June 16, 2025, 1:53am UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/72 "2025-06-16T01:53:32Z")

</div>

Thanks @pturmel, you're right, it would stall the script if something else has taken the lock already and seeing as though it's an unnecessary import it's not the best idea.

Referencing this as I had to do some digging into how it works.

> **[Chapter 19: Concurrency — Definitive Guide to Jython latest documentation](https://jython.readthedocs.io/en/latest/Concurrency/#module-import-lock)**

I also spent way too long looking at some of your example code [https://www.automation-pros.com/ignition/](https://www.automation-pros.com/ignition/) Thank you for making that available.

---

<div class="post-metadata">

**Author:** ![ckotadiya](https://avatars.discourse-cdn.com/v4/letter/c/a698b9/32.png) [@ckotadiya](https://forum.inductiveautomation.com/u/ckotadiya)\
**Post date:** [June 24, 2025, 7:32am UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/73 "2025-06-24T07:32:10Z")

</div>

> [@kgamble](#):
>
> We use Tailwind for most of our CSS at this point, at first it felt like a bit of a stretch because it's complicated. However once you get into it, being able to do things like `md:hidden` and just have things automagically get hidden on larger screens is insanely useful. (This also makes CSS easier when porting from Figma). We also manage an internal container that acts as a tailwind compiler, so that we can only compile what we are using, instead of the full tailwind stylesheet. Unfortunately this ones not public, because it includes some special sauce for custom themes we leverage pretty heavily.

Can you elaborate using of tailwind css in perspective?

---

<div class="post-metadata">

**Author:** ![Jay\_Jain](https://avatars.discourse-cdn.com/v4/letter/j/ed655f/32.png) [@Jay\_Jain](https://forum.inductiveautomation.com/u/Jay_Jain)\
**Post date:** [June 24, 2025, 11:54am UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/74 "2025-06-24T11:54:01Z")

</div>

> [@ckotadiya](#):
>
> Can you elaborate using of tailwind css in perspective?

+1

---

<div class="post-metadata">

**Author:** ![gnguyen](https://avatars.discourse-cdn.com/v4/letter/g/41988e/32.png) [@gnguyen](https://forum.inductiveautomation.com/u/gnguyen)\
**Post date:** [July 1, 2025, 9:26am UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/75 "2025-07-01T09:26:54Z")

</div>

> [@kgamble](#):
>
> We also manage an internal container that acts as a tailwind compiler

Very interested in that. Can you share more?

---

<div class="post-metadata">

**Author:** ![louagejasper](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/louagejasper/32/86311_2.png) [@louagejasper](https://forum.inductiveautomation.com/u/louagejasper)\
**Post date:** [October 8, 2025, 7:24pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/76 "2025-10-08T19:24:48Z")

</div>

It’s been a while, but I finally got to testing this auto-scan with the Flint extension. It does not seem to work.

I put these settings in my workspace:

```python
{
    "ignitionFlint.sslVerify": false,
    "ignitionFlint.ignitionGateways": [
        
        {
            "label": "local",
            "address": "http://localhost:8088", 
            "projectPaths": [ 
              "../"
            ],
            "updateDesignerOnSave": true,
            "forceUpdateDesigner": true,
            "supportsProjectScanEndpoint": true
        }
    ]
}

```

Since my project is my workspace, I'm not sure what to put in projectPaths.  
@kgamble any suggestions?

---

<div class="post-metadata">

**Author:** ![louagejasper](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/louagejasper/32/86311_2.png) [@louagejasper](https://forum.inductiveautomation.com/u/louagejasper)\
**Post date:** [October 16, 2025, 11:54am UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/77 "2025-10-16T11:54:04Z")

</div>

Also @kgamble , is there a way to get VSCode stop underlining the first part of a function call? (f.e. 'system.').

---

<div class="post-metadata">

**Author:** ![aaronrai24](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/aaronrai24/32/87248_2.png) [@aaronrai24](https://forum.inductiveautomation.com/u/aaronrai24)\
**Post date:** [October 16, 2025, 3:13pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/78 "2025-10-16T15:13:02Z")

</div>

@louagejasper the projectPaths should be the relative path where your ignition project is in your file system(check screenshot). If you go to Help\>Toggle Developer Tools in VSCode you can see a console, this is helpful for debugging if the project update is being sent or erroring out. Can you try opening that console and then saving in a project library script and see if any errors are logged?

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/2/e2726dfe1371a84f17b56d9bb73a2a6ad4e508ea.png)

---

<div class="post-metadata">

**Author:** ![louagejasper](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/louagejasper/32/86311_2.png) [@louagejasper](https://forum.inductiveautomation.com/u/louagejasper)\
**Post date:** [October 17, 2025, 1:56pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/79 "2025-10-17T13:56:25Z")

</div>

Thanks for your reply!  
What if I want to just open the project folder, what would be the path if I am in the project folder?  
I tried "", "/", but no success:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/b/abd2e4168c2ba954af16413e1c6faa426539e3d7.png)

I also tried to put .vscode in a parentfolder, and put this in:

```python
{
    "ignitionFlint.sslVerify": false,
    "ignitionFlint.ignitionGateways": [
        
        {
            "label": "local",
            "address": "http://localhost:8088", 
            "projectPaths": [ 
              "/ignition-data/projects/proferro"
            ],
            "updateDesignerOnSave": true,
            "forceUpdateDesigner": true,
            "supportsProjectScanEndpoint": true
        }
    ]
}

```

But that gave the same results.

Do you guys mount the project folders separately from the data volume? Your setup looks interesting!

---

<div class="post-metadata">

**Author:** ![swhite](https://avatars.discourse-cdn.com/v4/letter/s/8797f3/32.png) [@swhite](https://forum.inductiveautomation.com/u/swhite)\
**Post date:** [October 19, 2025, 7:15pm UTC](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759/80 "2025-10-19T19:15:18Z")

</div>

I created a VBA script in excel on a popup form to create json for tag import.

This helped speed up exporting alarms from HMI, cleanup in excel, to prepare for import.

[Previous page](https://forum.inductiveautomation.com/t/what-external-tools-do-you-use-for-ignition-development-and-why/93759.md?page=3)