**Author:** ![hewking32](https://avatars.discourse-cdn.com/v4/letter/h/b5ac83/32.png) [@hewking32](https://forum.inductiveautomation.com/u/hewking32)\
**Post date:** [June 5, 2023, 12:50pm UTC](https://forum.inductiveautomation.com/t/what-steps-are-required-to-transition-from-ignition-edge-to-full-ignition-gateway/74560/1 "2023-06-05T12:50:46Z")

</div>

Hi All  
I wonder what are the steps required if I were to incorporate Ignition edge gateway into full gateway?  
Are you aware of any gotchas?  
The full gateway is meant to do what old edge gateway was doing + additional functionality provided by the full gateway.  
Regards

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 5, 2023, 12:59pm UTC](https://forum.inductiveautomation.com/t/what-steps-are-required-to-transition-from-ignition-edge-to-full-ignition-gateway/74560/2 "2023-06-05T12:59:28Z")

</div>

Almost trivial, IIRC (haven't done that in quite a while). Restore an Edge gateway backup with the command line while the new Ignition install is stopped. Remove the "edition" setting from Ignition.conf. Use the password reset tool to cause recommissioning (might not be necessary). Start back up.

---

<div class="post-metadata">

**Author:** ![hewking32](https://avatars.discourse-cdn.com/v4/letter/h/b5ac83/32.png) [@hewking32](https://forum.inductiveautomation.com/u/hewking32)\
**Post date:** [June 5, 2023, 4:22pm UTC](https://forum.inductiveautomation.com/t/what-steps-are-required-to-transition-from-ignition-edge-to-full-ignition-gateway/74560/3 "2023-06-05T16:22:58Z")

</div>

thanks a lot Phil

---

<div class="post-metadata">

**Author:** ![hewking32](https://avatars.discourse-cdn.com/v4/letter/h/b5ac83/32.png) [@hewking32](https://forum.inductiveautomation.com/u/hewking32)\
**Post date:** [June 8, 2023, 10:49am UTC](https://forum.inductiveautomation.com/t/what-steps-are-required-to-transition-from-ignition-edge-to-full-ignition-gateway/74560/4 "2023-06-08T10:49:58Z")

</div>

i assume simple visio project export from edge to full ignition will also work ?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 8, 2023, 12:09pm UTC](https://forum.inductiveautomation.com/t/what-steps-are-required-to-transition-from-ignition-edge-to-full-ignition-gateway/74560/5 "2023-06-08T12:09:21Z")

</div>

Should, yes.