# Which OPC server for B&R PowerPanel PP500?

**URL:** <https://forum.inductiveautomation.com/t/which-opc-server-for-b-r-powerpanel-pp500/109592>\
**Category:** General Discussion\
**Created:** [August 11, 2025, 4:37pm UTC](https://forum.inductiveautomation.com/t/which-opc-server-for-b-r-powerpanel-pp500/109592 "2025-08-11T16:37:09Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [August 11, 2025, 4:37pm UTC](https://forum.inductiveautomation.com/t/which-opc-server-for-b-r-powerpanel-pp500/109592/1 "2025-08-11T16:37:09Z")

</div>

I'm attempting to assist in reading data from a B&R Automation PowerPanel PP500. The gateway has B&R PVI Server, OPC-DA COM Connection, software installed (but the licence key is no longer plugged into the gateway so there is a search taking place).

I did some configuration on this some years ago and remember that the network connection configuration was really quirky as if B&R were running their own network address scheme on top of Ethernet. Each device (including programming devices) had to have a unique B&R address.

Anyway, if they have to replace the PVI Server, what would anyone recommend? KepserverEx doesn't seem to support B&R. I can't find anything on the [br-automation.com](http://br-automation.com) website.

Thanks.

---

<div class="post-metadata">

**Author:** ![David\_Stone](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/david_stone/32/79749_2.png) [@David\_Stone](https://forum.inductiveautomation.com/u/David_Stone)\
**Post date:** [August 12, 2025, 11:17am UTC](https://forum.inductiveautomation.com/t/which-opc-server-for-b-r-powerpanel-pp500/109592/2 "2025-08-12T11:17:48Z")

</div>

B&R has a fully featured OPC-UA server built into the plc, not the HMI, if the visualisation is the web style that is set up on the hmi, it should be using OPC-UA for the tag comms. If it’s the old one, you can enable it in the plc if you have the original plc project and it’s new enough.

---

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [August 12, 2025, 1:49pm UTC](https://forum.inductiveautomation.com/t/which-opc-server-for-b-r-powerpanel-pp500/109592/3 "2025-08-12T13:49:51Z")

</div>

Thanks, David.  
The response from the German machine builder is,

> The B&R Power Panel 500 supports only OPC DA. But for your case you need OPC UA and that’s not compatible with the PP500.

I presume that the PLC doesn't allow a remote OPC server to read values in the way that Ignition's A-B driver can read an A-B PLC.

---

<div class="post-metadata">

**Author:** ![David\_Stone](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/david_stone/32/79749_2.png) [@David\_Stone](https://forum.inductiveautomation.com/u/David_Stone)\
**Post date:** [August 12, 2025, 1:51pm UTC](https://forum.inductiveautomation.com/t/which-opc-server-for-b-r-powerpanel-pp500/109592/4 "2025-08-12T13:51:57Z")

</div>

Probably out of luck. New panel time? Customers like shiny?