# Write Tag from designer to Automate

**URL:** <https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443>\
**Category:** Ignition\
**Created:** [January 27, 2022, 3:01pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443 "2022-01-27T15:01:06Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![r.relouzat](https://avatars.discourse-cdn.com/v4/letter/r/7cd45c/32.png) [@r.relouzat](https://forum.inductiveautomation.com/u/r.relouzat)\
**Post date:** [January 27, 2022, 3:01pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/1 "2022-01-27T15:01:06Z")

</div>

Hello,  
i didn’t find any topics about, let alone with any good concils.  
My question here is, how can i write and send tags from Edit Binding to Ip (Automate):

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/9/49a6695d6d09ccddaf7c556707209997fd3c9dc9.png)  
regards

---

<div class="post-metadata">

**Author:** ![victordcq](https://avatars.discourse-cdn.com/v4/letter/v/f6c823/32.png) [@victordcq](https://forum.inductiveautomation.com/u/victordcq)\
**Post date:** [January 27, 2022, 3:25pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/2 "2022-01-27T15:25:39Z")

</div>

Can you show the details of the pop and the logs of the error

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 27, 2022, 3:31pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/3 "2022-01-27T15:31:42Z")

</div>

Is it a Siemens PLC using the Siemens driver (guessing from the device name)? If so, `HR999` is not a valid [OPC Item Address](https://docs.inductiveautomation.com/pages/viewpage.action?pageId=72418224#Siemens-ConfiguringSiemensAddressing). Also, you have a data type of “Integer Array” which is not doing what you think (it is treating a single 16-bit register as an array of _ **bits** _).

Please describe the data as organized in the PLC for us. Then we can help you get the data to move back and forth with the OPC Quick Client. Only after that is verified do you go on to make your UI.

---

<div class="post-metadata">

**Author:** ![r.relouzat](https://avatars.discourse-cdn.com/v4/letter/r/7cd45c/32.png) [@r.relouzat](https://forum.inductiveautomation.com/u/r.relouzat)\
**Post date:** [January 27, 2022, 4:36pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/4 "2022-01-27T16:36:56Z")

</div>

We have two PLCs connected in Stand-by,  
The PLC Siemens S7-1500R/H-System\_1, CPU 1517H-3 PN is a server which provides an array size of 1001 words,  
The 650th words are read on equipment by the Siemens PLC,  
They, HR0 to HR650, are seen as read-only from the point of view of Ignition, Ignition must be able to write words to PLC between HR651 and HR1000 words.

My Data Type look like ok, i actually need to send one word only on HR999  
Regards

---

<div class="post-metadata">

**Author:** ![r.relouzat](https://avatars.discourse-cdn.com/v4/letter/r/7cd45c/32.png) [@r.relouzat](https://forum.inductiveautomation.com/u/r.relouzat)\
**Post date:** [January 27, 2022, 4:37pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/5 "2022-01-27T16:37:27Z")

</div>

Sorry i’m a beginner, i don’t know where to find the logs yet

---

<div class="post-metadata">

**Author:** ![victordcq](https://avatars.discourse-cdn.com/v4/letter/v/f6c823/32.png) [@victordcq](https://forum.inductiveautomation.com/u/victordcq)\
**Post date:** [January 28, 2022, 7:32am UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/6 "2022-01-28T07:32:29Z")

</div>

`http://<yourwebserver>:<yourport>/web/status/diag.logviewer`  
`http://localhost:8088/web/status/diag.logviewer`

---

<div class="post-metadata">

**Author:** ![r.relouzat](https://avatars.discourse-cdn.com/v4/letter/r/7cd45c/32.png) [@r.relouzat](https://forum.inductiveautomation.com/u/r.relouzat)\
**Post date:** [January 28, 2022, 10:19am UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/8 "2022-01-28T10:19:15Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/e/ce1a5b9d577ef52c7d1329c3b46d944f9738ab46.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/8/f8d4f9e3a8a0656032254d3e10250b62e2520d48.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 28, 2022, 12:48pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/9 "2022-01-28T12:48:51Z")

</div>

Did you deliberately use the Modbus driver for your Siemens PLC? The error is the target device deliberately rejecting the register number as invalid. Look in your PLC for the problem.

---

<div class="post-metadata">

**Author:** ![r.relouzat](https://avatars.discourse-cdn.com/v4/letter/r/7cd45c/32.png) [@r.relouzat](https://forum.inductiveautomation.com/u/r.relouzat)\
**Post date:** [January 31, 2022, 4:40pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/10 "2022-01-31T16:40:37Z")

</div>

Hello,  
No i didn’t deliberately use the Modbus driver, but each time i try to use the Siemens PLC one then i loose the connection with it. Maybe i need hand on it.  
Regards

---

<div class="post-metadata">

**Author:** ![r.relouzat](https://avatars.discourse-cdn.com/v4/letter/r/7cd45c/32.png) [@r.relouzat](https://forum.inductiveautomation.com/u/r.relouzat)\
**Post date:** [February 1, 2022, 5:13pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/11 "2022-02-01T17:13:46Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/e/4eea9e380d0dcfea91739375abeb655d90d849da.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/d/1d28e30a01492ab1479b74c2fa2f357c8f7633dd.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/8/5867728d42cfde88cd376031798c01ff7b5b22a9.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/b/9b0a51d2f17c5eb9df96e305240df704f8a85935.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/0/20936f72d58a043e839c74e82d225edafff5c44c.png)  
Please where i did en error

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 1, 2022, 5:59pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/12 "2022-02-01T17:59:43Z")

</div>

HR999 is not a valid address for the Siemens driver. As I noted five days ago.

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [February 1, 2022, 6:29pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/13 "2022-02-01T18:29:04Z")

</div>

> [@r.relouzat](#):
>
> They, HR0 to HR650, are seen as read-only from the point of view of Ignition, Ignition must be able to write words to PLC between HR651 and HR1000 words.

In the Siemens PLC, there is **NO** HRxxx... Where did you find these HRs...?

---

<div class="post-metadata">

**Author:** ![r.relouzat](https://avatars.discourse-cdn.com/v4/letter/r/7cd45c/32.png) [@r.relouzat](https://forum.inductiveautomation.com/u/r.relouzat)\
**Post date:** [March 29, 2022, 4:38pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/14 "2022-03-29T16:38:37Z")

</div>

Hello, my coworkers and i had connected till this afternoon with our device S71517h3pn with Type of Modbus TCP, but for any reason we lost it, the set up with Modbus TCP which is mandatory because we use two redundancy PLC (system), so we must to use the Modbus TCP.  
Can you help us to know how we could connect back

---

<div class="post-metadata">

**Author:** ![kvane](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kvane/32/22228_2.png) [@kvane](https://forum.inductiveautomation.com/u/kvane)\
**Post date:** [March 29, 2022, 4:57pm UTC](https://forum.inductiveautomation.com/t/write-tag-from-designer-to-automate/55443/15 "2022-03-29T16:57:17Z")

</div>

You should consider contacting [Inductive Automation Support](https://inductiveautomation.com/support/home/). While the forums are a great resource for knowledge sharing and basic troubleshooting advice - it is not an ideal resource for troubleshooting of this nature.