## [\[IGN-2903\] Get row selected in Alarm Journal Table](https://forum.inductiveautomation.com/t/ign-2903-get-row-selected-in-alarm-journal-table/59776)

<div class="topic-metadata">

**Author:** [@liam1](https://forum.inductiveautomation.com/u/liam1)\
**Replies:** 16\
**Last updated:** [October 22, 2026, 12:04pm UTC](https://forum.inductiveautomation.com/t/ign-2903-get-row-selected-in-alarm-journal-table/59776 "2026-10-22T12:04:56Z")

</div>

Hi all, How to I get the row data when a user selects/clicks on one from the Alarm Journal table? Im trying to get the uuid and timestamp of the selected row.

---

## [\[FEATURE-14735\] Perspective Time Series Chart Y-Axis Label](https://forum.inductiveautomation.com/t/feature-14735-perspective-time-series-chart-y-axis-label/29253)

<div class="topic-metadata">

**Author:** [@ray.crowder](https://forum.inductiveautomation.com/u/ray.crowder)\
**Replies:** 9\
**Last updated:** [October 16, 2026, 10:59pm UTC](https://forum.inductiveautomation.com/t/feature-14735-perspective-time-series-chart-y-axis-label/29253 "2026-10-16T22:59:40Z")

</div>

Does anyone know which property to change/set/add to change the label of the y axis on the time series chart component?

---

## [Examples for setting up SAML IDP profiles](https://forum.inductiveautomation.com/t/examples-for-setting-up-saml-idp-profiles/25112)

<div class="topic-metadata">

**Author:** [@mitchell-ACS](https://forum.inductiveautomation.com/u/mitchell-ACS)\
**Replies:** 10\
**Last updated:** [October 1, 2026, 6:42pm UTC](https://forum.inductiveautomation.com/t/examples-for-setting-up-saml-idp-profiles/25112 "2026-10-01T18:42:17Z")

</div>

Can we get some examples of how to set up different identity providers? I’m very excited about the idea of enabling MFA for my projects but the lingo is over my head and the configuration process has me lost. I thought…

---

## [Editing Perspective table with allowEditOn single-click still takes two clicks](https://forum.inductiveautomation.com/t/editing-perspective-table-with-allowediton-single-click-still-takes-two-clicks/30446)

<div class="topic-metadata">

**Author:** [@bkarabinchak.psi](https://forum.inductiveautomation.com/u/bkarabinchak.psi)\
**Replies:** 10\
**Last updated:** [September 29, 2026, 6:54am UTC](https://forum.inductiveautomation.com/t/editing-perspective-table-with-allowediton-single-click-still-takes-two-clicks/30446 "2026-09-29T06:54:00Z")

</div>

I have a table with two columns that are editable, a boolean and a string. I set the onCellEdit field to “single-click” however the real functionality seems to be click once to select the row, then click again to check …

---

## [Ignition Gateway Connection:Faulted](https://forum.inductiveautomation.com/t/ignition-gateway-connection-faulted/117114)

<div class="topic-metadata">

**Author:** [@s.muley](https://forum.inductiveautomation.com/u/s.muley)\
**Replies:** 2\
**Last updated:** [September 17, 2026, 2:09pm UTC](https://forum.inductiveautomation.com/t/ignition-gateway-connection-faulted/117114 "2026-09-17T14:09:18Z")

</div>

Hi, I am facing issue with Ignition Gateway . Status is faulted. says A "loopback" connection to the Ignition OPC UA server running on this gateway. How i recover this problem. Thank you in advance.

---

## [Teledyne ISCO Signature Flow Meter - Connection to Ignition keeps dropping out](https://forum.inductiveautomation.com/t/teledyne-isco-signature-flow-meter-connection-to-ignition-keeps-dropping-out/106644)

<div class="topic-metadata">

**Author:** [@jparsons](https://forum.inductiveautomation.com/u/jparsons)\
**Replies:** 4\
**Last updated:** [August 31, 2026, 2:48pm UTC](https://forum.inductiveautomation.com/t/teledyne-isco-signature-flow-meter-connection-to-ignition-keeps-dropping-out/106644 "2026-08-31T14:48:42Z")

</div>

I have a Teledyne Isco Flow meter connected via Modbus TCP that keeps dropping out every few seconds from Ignition. I have pinged it from the local network with no issues and pinged it from the ignition network with no i…

---

## [Ignition Designer Launcher Connection Exception Issue](https://forum.inductiveautomation.com/t/ignition-designer-launcher-connection-exception-issue/29776)

<div class="topic-metadata">

**Author:** [@sahibdeep.sodhi](https://forum.inductiveautomation.com/u/sahibdeep.sodhi)\
**Replies:** 18\
**Last updated:** [August 10, 2026, 1:52pm UTC](https://forum.inductiveautomation.com/t/ignition-designer-launcher-connection-exception-issue/29776 "2026-08-10T13:52:01Z")

</div>

When trying to connect to my Ignition Gateway from Ignition Designer Launcher i get the following error: Error Launching Application: ConnectException: Connection refused: connect I am using CentOS 7 linux server with…

---

## [OPC-UA client - Subscription ok in Ignition but not present in OPC-UA server](https://forum.inductiveautomation.com/t/opc-ua-client-subscription-ok-in-ignition-but-not-present-in-opc-ua-server/48003)

<div class="topic-metadata">

**Author:** [@chi](https://forum.inductiveautomation.com/u/chi)\
**Replies:** 25\
**Last updated:** [August 7, 2026, 3:13pm UTC](https://forum.inductiveautomation.com/t/opc-ua-client-subscription-ok-in-ignition-but-not-present-in-opc-ua-server/48003 "2026-08-07T15:13:46Z")

</div>

I have a strange problem with Ignition’s OPC-UA client. Some tags stop updating after working for some days. In the diagnostics i can see that Ignition thinks it has a subscription, but that subscription ist not present …

---

## [How to write the script of alarm notification to show in channel of microsoft teams?](https://forum.inductiveautomation.com/t/how-to-write-the-script-of-alarm-notification-to-show-in-channel-of-microsoft-teams/50507)

<div class="topic-metadata">

**Author:** [@apiraksr](https://forum.inductiveautomation.com/u/apiraksr)\
**Replies:** 7\
**Last updated:** [July 30, 2026, 12:36pm UTC](https://forum.inductiveautomation.com/t/how-to-write-the-script-of-alarm-notification-to-show-in-channel-of-microsoft-teams/50507 "2026-07-30T12:36:20Z")

</div>

I would like to use alarm notification. Could you share script for me,please?

---

## [Sync warning: Unable to send updates to client](https://forum.inductiveautomation.com/t/sync-warning-unable-to-send-updates-to-client/54461)

<div class="topic-metadata">

**Author:** [@nathan1](https://forum.inductiveautomation.com/u/nathan1)\
**Replies:** 39\
**Last updated:** [July 30, 2026, 1:17am UTC](https://forum.inductiveautomation.com/t/sync-warning-unable-to-send-updates-to-client/54461 "2026-07-30T01:17:03Z")

</div>

Hello. We are receiving this warning every second in the logs and was curious if there is a way to stop it. It doesn't seem to be affecting anything but makes it difficult to read incoming messages. We are running 8.1.12 …

---

## [Ignition in multiple facilities](https://forum.inductiveautomation.com/t/ignition-in-multiple-facilities/116546)

<div class="topic-metadata">

**Author:** [@nz839](https://forum.inductiveautomation.com/u/nz839)\
**Replies:** 5\
**Last updated:** [July 28, 2026, 3:07pm UTC](https://forum.inductiveautomation.com/t/ignition-in-multiple-facilities/116546 "2026-07-28T15:07:43Z")

</div>

Hello Everyone, I'm trying to get data from another site of my company but there is a doubt about licences. All of my sites are in the same network and I want to get data from every plant to a centralized Ignition Gatewa…

---

## [Reference parent component custom property](https://forum.inductiveautomation.com/t/reference-parent-component-custom-property/47549)

<div class="topic-metadata">

**Author:** [@steMos](https://forum.inductiveautomation.com/u/steMos)\
**Replies:** 2\
**Last updated:** [July 27, 2026, 10:35pm UTC](https://forum.inductiveautomation.com/t/reference-parent-component-custom-property/47549 "2026-07-27T22:35:13Z")

</div>

Hi all, I’ve tried to look through the forum but I can’t figure out if there is the possibility to have relative custom properties paths in Vision. There is a way to reference a “parent” custom property without using th…

---

## [Drawing Element inside of Perspective - where to find?](https://forum.inductiveautomation.com/t/drawing-element-inside-of-perspective-where-to-find/34421)

<div class="topic-metadata">

**Author:** [@DavidB](https://forum.inductiveautomation.com/u/DavidB)\
**Replies:** 3\
**Last updated:** [July 9, 2026, 4:24pm UTC](https://forum.inductiveautomation.com/t/drawing-element-inside-of-perspective-where-to-find/34421 "2026-07-09T16:24:07Z")

</div>

Hi, I’m trying to produce some proof of concept HMIs and throughout my internet searching have come across Ignition/Perspective - and the solution looks really promising for my needs (this isn’t my normal area of work). …

---

## [Ignition Machine Learning](https://forum.inductiveautomation.com/t/ignition-machine-learning/114992)

<div class="topic-metadata">

**Author:** [@kennethandradeom](https://forum.inductiveautomation.com/u/kennethandradeom)\
**Replies:** 2\
**Last updated:** [July 9, 2026, 12:32am UTC](https://forum.inductiveautomation.com/t/ignition-machine-learning/114992 "2026-07-09T00:32:24Z")

</div>

Hi, my name is Kenneth, I am working with Ignition Machine Learning Manager and I have historical tag data (temperature and humidity) collected over several months. My goal is to build a model that can predict future va…

---

## [\[IGN-16741\] Received prop sync for missing view](https://forum.inductiveautomation.com/t/ign-16741-received-prop-sync-for-missing-view/50674)

<div class="topic-metadata">

**Author:** [@paul.longtine](https://forum.inductiveautomation.com/u/paul.longtine)\
**Replies:** 12\
**Last updated:** [June 30, 2026, 1:14pm UTC](https://forum.inductiveautomation.com/t/ign-16741-received-prop-sync-for-missing-view/50674 "2026-06-30T13:14:15Z")

</div>

Every so often our Perspective project runs into log messages scoped at perspective.ClientSession with a message of Received prop sync for missing view. What scenario would trigger this message on the gateway? Is a clie…

---

## [Huge number of Alarm records in database after starting Ignition Gateway](https://forum.inductiveautomation.com/t/huge-number-of-alarm-records-in-database-after-starting-ignition-gateway/108307)

<div class="topic-metadata">

**Author:** [@iscrac](https://forum.inductiveautomation.com/u/iscrac)\
**Replies:** 6\
**Last updated:** [June 22, 2026, 8:38pm UTC](https://forum.inductiveautomation.com/t/huge-number-of-alarm-records-in-database-after-starting-ignition-gateway/108307 "2026-06-22T20:38:12Z")

</div>

Hi! I have a long time issue with alarm records to database after each Ignition Gateway start/restart Actually, when I start Ignition, so from every alarm tag I have record to database even if alarm is not active now. …

---

## [SerializationException caused by PMIButton in HashMap during open a window (Ignition 8.0.10)](https://forum.inductiveautomation.com/t/serializationexception-caused-by-pmibutton-in-hashmap-during-open-a-window-ignition-8-0-10/116005)

<div class="topic-metadata">

**Author:** [@info2](https://forum.inductiveautomation.com/u/info2)\
**Replies:** 4\
**Last updated:** [June 17, 2026, 2:52pm UTC](https://forum.inductiveautomation.com/t/serializationexception-caused-by-pmibutton-in-hashmap-during-open-a-window-ignition-8-0-10/116005 "2026-06-17T14:52:57Z")

</div>

Hello everyone, I'm experiencing a serialization error in one of my projects and I'm trying to understand the root cause. Error invoking \[HashMap\]{PMIButton: Button=\[com.inductiveautomation.factorypmi.application.bindi…

---

## [Ignition 8.0.10 - Vision window opens in runtime but cannot be opened in Designer](https://forum.inductiveautomation.com/t/ignition-8-0-10-vision-window-opens-in-runtime-but-cannot-be-opened-in-designer/116027)

<div class="topic-metadata">

**Author:** [@mori.luca](https://forum.inductiveautomation.com/u/mori.luca)\
**Replies:** 2\
**Last updated:** [June 17, 2026, 12:25pm UTC](https://forum.inductiveautomation.com/t/ignition-8-0-10-vision-window-opens-in-runtime-but-cannot-be-opened-in-designer/116027 "2026-06-17T12:25:41Z")

</div>

Hi everyone, I’m working on a legacy Vision project running on Ignition 8.0.10. The application runtime/client works correctly since 2020 and the affected window functions normally during runtime, but the Designer cann…

---

## [Redundant Failover Http Redirection - Perspective](https://forum.inductiveautomation.com/t/redundant-failover-http-redirection-perspective/37133)

<div class="topic-metadata">

**Author:** [@scott.stamps](https://forum.inductiveautomation.com/u/scott.stamps)\
**Replies:** 11\
**Last updated:** [June 9, 2026, 9:04pm UTC](https://forum.inductiveautomation.com/t/redundant-failover-http-redirection-perspective/37133 "2026-06-09T21:04:46Z")

</div>

All - we recently set up and tested our Ignition redundancy (forced a failover). Everything worked very well except for Perspective. We expected inbound requests for Perspective projects to be redirected, yet they were n…

---

## [Siemens s7 200 SMART](https://forum.inductiveautomation.com/t/siemens-s7-200-smart/39888)

<div class="topic-metadata">

**Author:** [@harigobu.gb](https://forum.inductiveautomation.com/u/harigobu.gb)\
**Replies:** 6\
**Last updated:** [June 8, 2026, 1:48pm UTC](https://forum.inductiveautomation.com/t/siemens-s7-200-smart/39888 "2026-06-08T13:48:02Z")

</div>

In one our plant we do have few S7 200 SMART plc’s. Is it possible to use any of the available Ignition device drivers for communicating with this PLC.

---

## [Upgrade to ignition 8.0.13 : Invalid configuration type hierarchy for node message?](https://forum.inductiveautomation.com/t/upgrade-to-ignition-8-0-13-invalid-configuration-type-hierarchy-for-node-message/35482)

<div class="topic-metadata">

**Author:** [@mazeyrat](https://forum.inductiveautomation.com/u/mazeyrat)\
**Replies:** 15\
**Last updated:** [May 28, 2026, 12:59pm UTC](https://forum.inductiveautomation.com/t/upgrade-to-ignition-8-0-13-invalid-configuration-type-hierarchy-for-node-message/35482 "2026-05-28T12:59:13Z")

</div>

I’ve upgraded a 8.0.12 gateway to 8.0.13, I have some message: INFO | jvm 1 | 2020/06/10 09:50:04 | W \[t.s.internaljson \] \[07:50:04\]: Invalid configuration type hierarchy for node '02dce1a3-f032-4a9c-b…

---

## [Can't save gateway scripts to specific project](https://forum.inductiveautomation.com/t/cant-save-gateway-scripts-to-specific-project/61274)

<div class="topic-metadata">

**Author:** [@Benjamin\_Kloosterman](https://forum.inductiveautomation.com/u/Benjamin_Kloosterman)\
**Replies:** 5\
**Last updated:** [May 21, 2026, 10:59pm UTC](https://forum.inductiveautomation.com/t/cant-save-gateway-scripts-to-specific-project/61274 "2026-05-21T22:59:29Z")

</div>

I have a customaers gateway that is running igniiton 8.0.9. It had some gateway timer scripts running on it for about two years. Yesterday it stopped working and the scripts had vanished from the gateway events page. The…

---

## [Perspective onActionPerformed vs onClick](https://forum.inductiveautomation.com/t/perspective-onactionperformed-vs-onclick/39469)

<div class="topic-metadata">

**Author:** [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Replies:** 3\
**Last updated:** [May 21, 2026, 1:29pm UTC](https://forum.inductiveautomation.com/t/perspective-onactionperformed-vs-onclick/39469 "2026-05-21T13:29:02Z")

</div>

What is the main difference in these events? I’ve been using onActionPerformed. But, noticed is some sample projects users were using onClick.

---

## [Perspective table auto size in flex](https://forum.inductiveautomation.com/t/perspective-table-auto-size-in-flex/39781)

<div class="topic-metadata">

**Author:** [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Replies:** 5\
**Last updated:** [May 14, 2026, 1:41pm UTC](https://forum.inductiveautomation.com/t/perspective-table-auto-size-in-flex/39781 "2026-05-14T13:41:25Z")

</div>

Perspective 8.0.16 I have a flex view and several flex containers inside that view (rows). What I would like is to have a table (in one of the flex containers) automatically grow and shrink. I want them to grow to the…

---

## [Converting Crystal Report formula to use in Ignition Designer](https://forum.inductiveautomation.com/t/converting-crystal-report-formula-to-use-in-ignition-designer/115438)

<div class="topic-metadata">

**Author:** [@l.rollins](https://forum.inductiveautomation.com/u/l.rollins)\
**Replies:** 4\
**Last updated:** [May 7, 2026, 4:40pm UTC](https://forum.inductiveautomation.com/t/converting-crystal-report-formula-to-use-in-ignition-designer/115438 "2026-05-07T16:40:52Z")

</div>

I have a CR formula that I want to use in Ignition. IF {GFSITMATT\_COPPERLIQ.ATTVALCOD\_0} \<\> "NONE" THEN extractstring({ATEXTRA\_COPPERLIQ.TEXTE\_0},'',' =') + "-" + extractstring({ATEXTRA\_COPPER.TEXTE\_0},'',' =') ELSE …

---

## [SNMP function for Ignition version 8](https://forum.inductiveautomation.com/t/snmp-function-for-ignition-version-8/35167)

<div class="topic-metadata">

**Author:** [@allnet](https://forum.inductiveautomation.com/u/allnet)\
**Replies:** 31\
**Last updated:** [April 27, 2026, 4:14am UTC](https://forum.inductiveautomation.com/t/snmp-function-for-ignition-version-8/35167 "2026-04-27T04:14:34Z")

</div>

Hi all. Here you have a simple SNMP function tested with v1/v2c devices under V8 As of now the only operation available is snmp Get and can be called by using system.snmp.snmpGet('community', 'address', port, 'OID') R…

---

## [Gateway Error executing historical tag read](https://forum.inductiveautomation.com/t/gateway-error-executing-historical-tag-read/58616)

<div class="topic-metadata">

**Author:** [@GOKULAKANNAN\_P](https://forum.inductiveautomation.com/u/GOKULAKANNAN_P)\
**Replies:** 6\
**Last updated:** [April 16, 2026, 3:52pm UTC](https://forum.inductiveautomation.com/t/gateway-error-executing-historical-tag-read/58616 "2026-04-16T15:52:50Z")

</div>

Hello, I got this error continuously in Gateway . I Used History tag in Easy chart component . Error: java.lang.IllegalArgumentException: Requested timestamp is previous to an already requested time. All requests …

---

## [Latency when using Ignition with PLC](https://forum.inductiveautomation.com/t/latency-when-using-ignition-with-plc/115039)

<div class="topic-metadata">

**Author:** [@onderhoud](https://forum.inductiveautomation.com/u/onderhoud)\
**Replies:** 5\
**Last updated:** [April 13, 2026, 3:06pm UTC](https://forum.inductiveautomation.com/t/latency-when-using-ignition-with-plc/115039 "2026-04-13T15:06:28Z")

</div>

Hi, We are working on an industrial machine where Ignition is used between the HMI and a PLC. We are experiencing noticeable latency when triggering commands such as start/stop from the HMI, which affects the consisten…

---

## [Perspective: Scripting a Momentary Button](https://forum.inductiveautomation.com/t/perspective-scripting-a-momentary-button/35684)

<div class="topic-metadata">

**Author:** [@AIO](https://forum.inductiveautomation.com/u/AIO)\
**Replies:** 7\
**Last updated:** [April 11, 2026, 10:15am UTC](https://forum.inductiveautomation.com/t/perspective-scripting-a-momentary-button/35684 "2026-04-11T10:15:11Z")

</div>

Hey folks, Ignition 8.0.7 I’m trying to implement a momentary button in Perspective, but the feature doesn’t appear to be available. The One-Shot Button documentation states, “If your PLC expects the HMI to reset the b…

---

## [Is there a way to stop alarms from being sent if the gateway restarts?](https://forum.inductiveautomation.com/t/is-there-a-way-to-stop-alarms-from-being-sent-if-the-gateway-restarts/59017)

<div class="topic-metadata">

**Author:** [@mSet](https://forum.inductiveautomation.com/u/mSet)\
**Replies:** 4\
**Last updated:** [April 9, 2026, 3:12pm UTC](https://forum.inductiveautomation.com/t/is-there-a-way-to-stop-alarms-from-being-sent-if-the-gateway-restarts/59017 "2026-04-09T15:12:01Z")

</div>

I haven’t been able to find a solution to prevent alarms being resent if the gateway restarts.