Generally not much since it's an 8.1.x to 8.1.x version, but you know... things can go wrong. People who are truly concerned about such things have separate dev/testing environments.
Make sure you take a gateway backup before the upgrade. It's relatively easy to get back to the version you were on if things go wrong.
1 Like
for my current version is not possible to communicate with KV-8000?
If you can use the onboard OPC UA server that the KV-8000 is supposed to have that will be an option. I don't know any more about that other than it's supposed to exist, you'll have to check the documentation. You would just make a direct OPC UA connection instead of using a driver.
oh right , i’ll try with upgrading the current version. i have a local server in my personal PC but i have the version 8.1.38 , the setup its only putting the IP Target of PLC?
First i’ll do tests on my PC
Kevin is suggesting that you enable the OPC-UA server in the PLC. Make a note of the settings and any security details.
In Ignition you create an OPC Connection (not a Device Connection).
If you use the Advanced Options you'll see a dialog like this,
... but steping through the prompts is usually easier.
What you're doing here is making Ignition a client of the OPC-UA server on the PLC. (Choose UA, not DA which is obsolete.)