Cannot run multiple Named Queries in 1 tag script
On your gateway page, config -> system -> gateway settings:
Things that are not related to a project, like tags, have no way of knowing where they should look for scripts. That's what the GSP is for: It tells them what project contains the scripts.
This means you can only have one GSP, so if you have scripts that need to be used by tags in several different projects, you'll need to gather them in one single project.
But, again, you shouldn't be using a tag value change for this kind of script. Use a gateway event. Gateway events belong to a project, and will know where to look for scripts.
I already had my projectname in the Gateway Scripting Project. I will give gateway event tag change a try
Did you take on any of @pascal.fragnoud 's advice yet?
Yes, all of them in fact. Nothing have worked. There is a bug with namedquries. This post that is 4 years old is about the same issue, but the workaround in that post no longer work:
Can't execute multiple runNamedQuery updates - Ignition - Inductive Automation Forum
I really hope someone have a solution otherwise I will have to create a new tag for each query i want to run and then just change the value of each tag.
If you took @pascal.fragnoud's advice, then you wouldn't be calling multiple consecutive named queries.
You would be calling a PrepQuery, a Named Query, and a Prep Query. In that order.
If you write the script in a generic fashion, and you use a Gateway Tag Change Script, then you can assign multiple tags to trigger the same script.
I run multiple named queries in a script with no issues...
Can you describe exactly which query works and which doesn't? In your original script, you only have 2 named queries. The others are runPrep.
Have you added logging to the script to check return values etc?
What does "doesn't work" mean ?
Is there anything in the logs ? Do you get wrong results ?
IIUC, transactions for named queries are distinct from transactions for other system.db queries. So, this approach with transactions would not ever work.
That isn't what I advised. This entire operation is unfit for tag events (on the tag). Use a project gateway tag change event.
Just to make it more clear. The first nameQuery:
system.db.runNamedQuery("WDE_System","NP/HI/25L/WD/OrderBreakdown/Insert_life_cycle", life_cycle_params)
Runs and insert data in my database. The second namequery:
system.db.runNamedQuery("WDE_System","NP/HI/25L/WD/OrderBreakdown/Insert_Material_Reservation", material_reservation_params)
Does not insert anything in my database, unless if I run the code in the script console. I do get this error:
Java Traceback:
  File "<input>", line 25, in <module>
	at com.inductiveautomation.ignition.common.TypeUtilities.coerce(TypeUtilities.java:1681)
	at com.inductiveautomation.ignition.common.script.builtin.PyArgumentMap.coerce(PyArgumentMap.java:130)
	at com.inductiveautomation.ignition.common.script.builtin.PyArgumentMap.interpretPyArgs(PyArgumentMap.java:82)
	at com.inductiveautomation.ignition.common.script.builtin.PyArgumentMap.interpretPyArgs(PyArgumentMap.java:40)
	at com.inductiveautomation.ignition.client.script.ClientDBUtilities.runNamedQuery(ClientDBUtilities.java:106)
java.lang.ClassCastException: java.lang.ClassCastException: Cannot coerce value 'NP/HI/25L/WD/OrderBreakdown/Insert_life_cycle' into type: interface java.util.Map
	at org.python.core.Py.JavaError(Py.java:545)
	at org.python.core.Py.JavaError(Py.java:536)
	at org.python.core.PyReflectedFunction.__call__(PyReflectedFunction.java:192)
	at com.inductiveautomation.ignition.common.script.ScriptManager$ReflectedInstanceFunction.__call__(ScriptManager.java:553)
	at org.python.core.PyObject.__call__(PyObject.java:494)
	at org.python.core.PyObject.__call__(PyObject.java:498)
	at org.python.pycode._pyx773.f$0(<input>:30)
	at org.python.pycode._pyx773.call_function(<input>)
	at org.python.core.PyTableCode.call(PyTableCode.java:173)
	at org.python.core.Py.runCode(Py.java:1703)
	at org.python.core.Py.exec(Py.java:1747)
	at org.python.util.PythonInterpreter.exec(PythonInterpreter.java:277)
	at org.python.util.InteractiveInterpreter.runcode(InteractiveInterpreter.java:130)
	at com.inductiveautomation.ignition.designer.gui.tools.jythonconsole.JythonConsole$ConsoleWorker.doInBackground(JythonConsole.java:628)
	at com.inductiveautomation.ignition.designer.gui.tools.jythonconsole.JythonConsole$ConsoleWorker.doInBackground(JythonConsole.java:616)
	at java.desktop/javax.swing.SwingWorker$1.call(Unknown Source)
	at java.desktop/javax.swing.SwingWorker.run(Unknown Source)
Caused by: java.lang.ClassCastException: Cannot coerce value 'NP/HI/25L/WD/OrderBreakdown/Insert_life_cycle' into type: interface java.util.Map
	at org.python.core.PyReflectedFunction.__call__(PyReflectedFunction.java:190)
	... 19 more
localOrderShopFloorOrderId = system.tag.readBlocking(["[NP_HI_25L_WDE_ProcessProvider]NP/HI/25L/WDE/OrderBreakdown/PAS-X/WDEDOWN/MatFlow_MATERIAL_CHECK_MESSAGE/shopFloorOrderId"])[0].value
bomTargetMaterialNumber = system.tag.readBlocking(["[NP_HI_25L_WDE_ProcessProvider]NP/HI/25L/WDE/OrderBreakdown/PAS-X/WDEDOWN/Transaction_DOWNLOAD/targetMaterialNumber"])[0].value
bomTargetBatchSize = system.tag.readBlocking(["[NP_HI_25L_WDE_ProcessProvider]NP/HI/25L/WDE/OrderBreakdown/PAS-X/WDEDOWN/Transaction_DOWNLOAD/targetBatchSize"])[0].value
query_select_target_source_item = """
SELECT [targetSourceItem]
FROM [NP_HI_25L_WD_DB].[dbo].[tblBillOfMaterials]
WHERE [targetMaterialNumber] = ? AND [targetBatchSize] = ?
bomTargetSourceItem = system.db.runPrepQuery(query_select_target_source_item, [bomTargetMaterialNumber, bomTargetBatchSize])
query_select_material_number = """
SELECT [materialNumber]
materialNumber = system.db.runPrepQuery(query_select_material_number, [bomTargetMaterialNumber, bomTargetBatchSize])
query_select_quantity = """
SELECT [loQuantity]
quantity = system.db.runPrepQuery(query_select_quantity, [bomTargetMaterialNumber, bomTargetBatchSize])
life_cycle_params = {"localOrderShopFloorOrderId": localOrderShopFloorOrderId, "lifeCycleName": 'LOCAL_ORDER',"lifeCycleStatus": 'RESERVED',"operatorComment": 'NONE',"createdBy": 'NVML',"archived": 0}
material_reservation_params = {"loShopFloorOrderId": localOrderShopFloorOrderId, "bomTargetMaterialNumber": bomTargetMaterialNumber,"bomTargetBatchSize": bomTargetBatchSize, "bomTargetSourceItem": bomTargetSourceItem[0]['targetSourceItem'],"bomMaterialNumber":materialNumber[0]['materialNumber'] , "reservedQuantity": quantity[0]['loQuantity'], "unitOfMesurementId": 'kg ac.ing.', "createdBy": 'NVML', "archived": 0}
Can you please show me how you are able to run multiple namedqueries in 1 tag?
Again,
The script console does not run in Gateway Scope, and so the function signature for system.db.runNamedQuery() is not the same.
The script console is not an appropriate place to for testing scripts that are going run in Gateway Scope. Unless you take steps to force functions to run in the appropriate scope.
The script consle runs in Vision Client Scope and so it uses the "Project Scope" signature, which doesn't accept the project argument. This is why you get the error.
It is expecting the second argument to be the params dictionary, but you're suppling it with the Named Query Path.
Nothing shows up in the logs. Only 1 namedquery is being executed in the tag script but both are being executed in the script console.
If I remove the first argument from the queries i get this error:
Java Traceback:
	at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.newGatewayException(GatewayInterface.java:360)
	at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.sendMessage(GatewayInterface.java:334)
	at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.sendMessage(GatewayInterface.java:287)
	at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.invoke(GatewayInterface.java:967)
	at com.inductiveautomation.ignition.designer.db.namedquery.DesignerNamedQueryManager.execute(DesignerNamedQueryManager.java:73)
	at com.inductiveautomation.ignition.designer.db.namedquery.DesignerNamedQueryManager.execute(DesignerNamedQueryManager.java:46)
	at com.inductiveautomation.ignition.client.script.ClientDBUtilities.runNamedQuery(ClientDBUtilities.java:118)
	at jdk.internal.reflect.GeneratedMethodAccessor269.invoke(Unknown Source)
com.inductiveautomation.ignition.client.gateway_interface.GatewayException: com.inductiveautomation.ignition.client.gateway_interface.GatewayException: com.microsoft.sqlserver.jdbc.SQLServerException: The statement did not return a result set.
	at org.python.core.PyObject.__call__(PyObject.java:477)
	at org.python.core.PyObject.__call__(PyObject.java:481)
	at org.python.pycode._pyx814.f$0(<input>:28)
	at org.python.pycode._pyx814.call_function(<input>)
Caused by: com.inductiveautomation.ignition.client.gateway_interface.GatewayException: com.microsoft.sqlserver.jdbc.SQLServerException: The statement did not return a result set.
	... 19 more
Caused by: java.lang.Exception: com.microsoft.sqlserver.jdbc.SQLServerException: The statement did not return a result set.
	at com.inductiveautomation.ignition.gateway.db.namedquery.NamedQueryExecutor$NamedQueryInstance.execute(NamedQueryExecutor.java:407)
	at com.inductiveautomation.ignition.gateway.db.namedquery.NamedQueryExecutor.execute(NamedQueryExecutor.java:196)
	at com.inductiveautomation.ignition.gateway.db.namedquery.GatewayNamedQueryManager.execute(GatewayNamedQueryManager.java:124)
	at com.inductiveautomation.ignition.gateway.servlets.gateway.functions.NamedQueryFunctions.executeNamedQuery(NamedQueryFunctions.java:67)
	at jdk.internal.reflect.GeneratedMethodAccessor199.invoke(null)
	at jdk.internal.reflect.DelegatingMethodAccessorImpl.invoke(null)
	at java.lang.reflect.Method.invoke(null)
	at com.inductiveautomation.ignition.gateway.servlets.gateway.AbstractGatewayFunction.invoke(AbstractGatewayFunction.java:228)
	at com.inductiveautomation.ignition.gateway.servlets.Gateway.doPost(Gateway.java:435)
	at javax.servlet.http.HttpServlet.service(HttpServlet.java:523)
	at javax.servlet.http.HttpServlet.service(HttpServlet.java:590)
	at com.inductiveautomation.ignition.gateway.bootstrap.MapServlet.service(MapServlet.java:86)
	at org.eclipse.jetty.servlet.ServletHolder$NotAsync.service(ServletHolder.java:1410)
	at org.eclipse.jetty.servlet.ServletHolder.handle(ServletHolder.java:764)
	at org.eclipse.jetty.servlet.ServletHandler$ChainEnd.doFilter(ServletHandler.java:1665)
	at org.eclipse.jetty.servlet.ServletHandler.doHandle(ServletHandler.java:527)
	at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:131)
	at org.eclipse.jetty.security.SecurityHandler.handle(SecurityHandler.java:598)
	at org.eclipse.jetty.server.handler.HandlerWrapper.handle(HandlerWrapper.java:122)
	at org.eclipse.jetty.server.handler.ScopedHandler.nextHandle(ScopedHandler.java:223)
	at org.eclipse.jetty.server.session.SessionHandler.doHandle(SessionHandler.java:1580)
	at org.eclipse.jetty.server.handler.ScopedHandler.nextHandle(ScopedHandler.java:221)
	at org.eclipse.jetty.server.handler.ContextHandler.doHandle(ContextHandler.java:1384)
	at org.eclipse.jetty.server.handler.ScopedHandler.nextScope(ScopedHandler.java:176)
	at org.eclipse.jetty.servlet.ServletHandler.doScope(ServletHandler.java:484)
	at org.eclipse.jetty.server.session.SessionHandler.doScope(SessionHandler.java:1553)
	at org.eclipse.jetty.server.handler.ScopedHandler.nextScope(ScopedHandler.java:174)
	at org.eclipse.jetty.server.handler.ContextHandler.doScope(ContextHandler.java:1306)
	at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:129)
	at com.inductiveautomation.catapult.handlers.RemoteHostNameLookupHandler.handle(RemoteHostNameLookupHandler.java:121)
	at org.eclipse.jetty.rewrite.handler.RewriteHandler.handle(RewriteHandler.java:301)
	at org.eclipse.jetty.server.handler.HandlerList.handle(HandlerList.java:51)
	at org.eclipse.jetty.server.handler.HandlerCollection.handle(HandlerCollection.java:141)
	at org.eclipse.jetty.server.Server.handle(Server.java:563)
	at org.eclipse.jetty.server.HttpChannel$RequestDispatchable.dispatch(HttpChannel.java:1598)
	at org.eclipse.jetty.server.HttpChannel.dispatch(HttpChannel.java:753)
	at org.eclipse.jetty.server.HttpChannel.handle(HttpChannel.java:501)
	at org.eclipse.jetty.server.HttpConnection.onFillable(HttpConnection.java:287)
	at org.eclipse.jetty.io.AbstractConnection$ReadCallback.succeeded(AbstractConnection.java:314)
	at org.eclipse.jetty.io.FillInterest.fillable(FillInterest.java:100)
	at org.eclipse.jetty.io.SelectableChannelEndPoint$1.run(SelectableChannelEndPoint.java:53)
	at org.eclipse.jetty.util.thread.strategy.AdaptiveExecutionStrategy.runTask(AdaptiveExecutionStrategy.java:421)
	at org.eclipse.jetty.util.thread.strategy.AdaptiveExecutionStrategy.consumeTask(AdaptiveExecutionStrategy.java:390)
	at org.eclipse.jetty.util.thread.strategy.AdaptiveExecutionStrategy.tryProduce(AdaptiveExecutionStrategy.java:277)
	at org.eclipse.jetty.util.thread.strategy.AdaptiveExecutionStrategy.run(AdaptiveExecutionStrategy.java:199)
	at org.eclipse.jetty.util.thread.ReservedThreadExecutor$ReservedThread.run(ReservedThreadExecutor.java:411)
	at org.eclipse.jetty.util.thread.QueuedThreadPool.runJob(QueuedThreadPool.java:969)
	at org.eclipse.jetty.util.thread.QueuedThreadPool$Runner.doRunJob(QueuedThreadPool.java:1194)
	at org.eclipse.jetty.util.thread.QueuedThreadPool$Runner.run(QueuedThreadPool.java:1149)
	at java.lang.Thread.run(null)
What should I do about the namedquery not returning a set? It is an insert query.
How is the Insert_life_cycle, query configured? Do you have it's Query Type set to Query or Update Query?
It is set to query,
It does not help to set it to update query. I have tested the query
An Insert Query, is an Update Query, it must be set to Update Query. That is what is causing the above error.
I still get the same error:
Did you save the project after making the change?
I am such an idiot. I feel so sorry for wasting your time. It all works now, I forgot to save the project after changing the query type. You saved my weekend.
I have no idea why it worked in the script console.