Ignition 8.0.12
Can you upload the logs somewhere? Those log messages appear to be out of orderā¦ not sure why.
If you can get the Wireshark capture of UaExpert writing to the same Node I think that will be useful at this point.
test3.zip (71.5 KB)
My logsā¦
Ignition_LM_Ignition_logs_20200508-1144.zip (2.2 MB)
Strange, UaExpert is actually writing an Int16 value instead. I have no idea why, though. I know you mentioned that this type is both an Enumeration and Short value, but that doesnāt make any sense - all enumerations are Int32 in OPC UA. Did you change this tagās type at some point from enum to Short/Int16?
I found!!!
Thanks, the problem was that the ENUM was not initiate as DINT in CODESYS projectā¦
1 Like