Bad. If the gateway experiences any heavy load at 4pm, this expression can miss the event. Especially if using fixed delay. If using fixed period, and the event that normally falls a 3:59:59 is slightly delayed, this can fire twice in a row. The chance is low, so you wouldn't be likely to see either problem often, but it would happen.

I would use something like this in a project script module:

from java.util import Date
lastTrigPath = '[default]some/path/to/datetime/tag'

# Simple function to convert any timestamp to the trigger point on the same day
def truncateToTrigger(ts):
	return Date(ts.year, ts.month, ts.date, 16, 0, 0)

# Check if time to run the triggered event.  Call from timer script
def checkTrigger():
	last = system.tag.read(lastTrigPath).value
	nextTrig = truncateToTrigger(last)
	if nextTrig.time < last.time:
		nextTrig = system.date.addDays(nextTrig, 1)
	now = Date()
	if nextTrig.time <= now.time:
		system.tag.write(lastTrigPath, now)
		# Do the trigger stuff here

Call project.something.checkTrigger() from a gateway timer script of the desired precision. It will not double fire, and will always fire if the event is late. Even if it's late due to a gateway reboot.