We do not have a profinet network. I would like to connect the 1215C CPU to the network our Ignition server is on via ethernet.
Are you referring to this section of the Ignition manual:
Considerations for 1200 and 1500 Devices
The following considerations and configurations changes must be made when using the S7-1200 and S7-1500 drivers:
- Only global DBs can be accessed.
- The optimized block access must be turned off.
- The access level must be "full" and the "connection mechanism" must allow GET/PUT.
- Reads and Writes can not be used in TM/CT areas.