How can I make the Ignition Maker Edition adapt to the speed of data transfer between Kepware and the software (matlab) , so that the data is not lost and is displayed correctly in the Ignition Maker Edition curve?

Ignition's primary use is for SCADA systems generally using OPC communications (such as Kepware's OPC servers). Typical scan rates would be 100 ms for a reasonably snappy HMI interface, to as slow as is adequate for data logging. 1 ms scan time seems unrealistic. You will push requests into the queue and it will handle them as best it can. It sounds like you are trying to use it as a (medium-)high-speed data aquisition system instead.

You might find this post helpful.