Ignition installation in Docker can't connect with Bacnet Device

You mean this one?

I should be pretty simple

  • IP address of the remote host,
  • port number for communication default 47808
  • device ID that the device have. Inn my case 2001
  • Write priority is on of 16 different priority's on the tag.
  • COV. Data clients subscribe to an object for COV reporting. The device monitors the value of the object property, monitors the subscription list and the change criteria. When the change criteria are met the devices sends notifications of the new value to the subscribers.

The typical that is wrong with bacnet is the BBMD setup when the devices is on different networks.
image

Introduction on BBMD

But I think it is setup right, everything works on the bacnet client.
The devices is auto discovered on the client.

This devices is auto discoverer
image

I can search for the devices with the IP address and port number.
This is how I connect bacnet devices to a kepware server. With IP and port nr.
image

I tried to change the
Broadcast Address to 10.80.4.255
From the manual. Broadcast Address A network address shared by other BACnet devices to send and receive UDP data.


And then It worked :slight_smile:

Thanks for your troubleshooting help. Then it looks like I'm in touch. Also, I hope this can be of help to others who apply for this

1 Like