I always forget about this...
Holy moly
Edit:
Updated results with tests using different CIP Connection sizes:
Test | Ext Access | CIP Connection Size | Tag Count | Sample Rate (ms) | Actual Sample Rate (ms) | Request Count | Overload |
---|---|---|---|---|---|---|---|
UDTs | All Read/Write | 500 | 6787 | 10 | 45.48 | 14 | 355% |
UDTs | All Read/Write | 4000 | 6787 | 10 | 10.06 | 2 | 1% |
AOI Local Tags (UDT) | All Read/Write | 500 | 6787 | 10 | 50.86 | 14 | 409% |
AOI Local Tags (UDT) | All Read/Write | 4000 | 6787 | 10 | 10.08 | 2 | 1% |
AOI Parameter Tags | All Read/Write except EnableIn/Out | 4000 | 6787 | 10 | 519.02 | 33 | 5090% |
Aliased UDT Array Elements | All Read/Write | 4000 | 6760 | 10 | 10.06 | 2 | 1% |
UDT Array Elements | All Read/Write | 4000 | 6787 | 10 | 10.06 | 2 | 1% |