Logging Boolean Tag
Bind the named query with parameters to your Perspective Table's props.data (as described above). In the binding configuration, select Dataset return format. Your table will show the raw results (with long integer milliseconds for t_stamp and t_next).
Once you see the raw results, there should be an icon next to props.data that opens the dataset editor. From there, click the "Copy to Clipboard" button.
Then reply here on the forum, paste that CSV content, re-highlight in the forum comment editor, then click the "Preformatted Text" button. The one that looks like this: </>
Im not seeing the data set return. I know I should know this. Thank you being patient.
You haven't provided bindings within the NQ binding for its parameters. For which I instructed you to create view custom parameters. (Each of those with expression bindings.)
Do not use return format "auto". Use "dataset" return format.
@pturmel
  • You are trying to add a custom prop to the view's root container. Don't. Define it at the view itself. (Click on the name of the view in the designer tree, then scroll to the "Custom" section of its properties.)
  • Do the end property first, because start needs it.
  • Name the property correctly before opening the binding dialog.
Didnt even realize i was on the root container.
Please fix key and key_1 to end and start. :man_shrugging:
ok fixed. So now in the data parameters change them to point to the customs?
"#NAMES"
"chargetime_ndx","AGV10","t_stamp","t_next"
"#TYPES"
"I","I","date","date"
"#ROWS","53"
"24","0","2024-07-31 01:59:38.377","2024-07-31 08:11:05.617"
"25","1","2024-07-31 08:11:05.617","2024-07-31 08:11:43.787"
"26","0","2024-07-31 08:11:43.787","2024-07-31 08:19:34.507"
"27","1","2024-07-31 08:19:34.507","2024-07-31 08:20:05.537"
"28","0","2024-07-31 08:20:05.537","2024-07-31 08:20:35.573"
"29","1","2024-07-31 08:20:35.573","2024-07-31 08:23:20.950"
"30","0","2024-07-31 08:23:20.950","2024-07-31 08:23:40.973"
"31","1","2024-07-31 08:23:40.973","2024-07-31 08:29:07.783"
"32","0","2024-07-31 08:29:07.783","2024-07-31 08:29:23.807"
"33","1","2024-07-31 08:29:23.807","2024-07-31 08:34:03.357"
"34","0","2024-07-31 08:34:03.357","2024-07-31 08:35:09.557"
"35","1","2024-07-31 08:35:09.557","2024-07-31 08:40:33.230"
"36","0","2024-07-31 08:40:33.230","2024-07-31 08:40:48.247"
"37","1","2024-07-31 08:40:48.247","2024-07-31 08:47:50.027"
"38","0","2024-07-31 08:47:50.027","2024-07-31 08:48:05.070"
"39","1","2024-07-31 08:48:05.070","2024-07-31 08:48:36.110"
"40","0","2024-07-31 08:48:36.110","2024-07-31 08:54:56.517"
"41","1","2024-07-31 08:54:56.517","2024-07-31 08:55:34.563"
"42","0","2024-07-31 08:55:34.563","2024-07-31 10:02:51.380"
"43","1","2024-07-31 10:02:51.380","2024-07-31 10:14:33.647"
"44","0","2024-07-31 10:14:33.647","2024-07-31 12:14:58.550"
"45","1","2024-07-31 12:14:58.550","2024-07-31 12:16:55.507"
"46","0","2024-07-31 12:16:55.507","2024-07-31 12:37:05.820"
"47","1","2024-07-31 12:37:05.820","2024-07-31 12:37:22.967"
"48","0","2024-07-31 12:37:22.967","2024-07-31 12:48:53.967"
"49","1","2024-07-31 12:48:53.967","2024-07-31 12:53:42.037"
"50","0","2024-07-31 12:53:42.037","2024-07-31 12:54:06.063"
"51","1","2024-07-31 12:54:06.063","2024-07-31 12:58:21.620"
"52","0","2024-07-31 12:58:21.620","2024-07-31 12:58:48.647"
"53","1","2024-07-31 12:58:48.647","2024-07-31 12:59:35.700"
"54","0","2024-07-31 12:59:35.700","2024-07-31 12:59:59.773"
"55","1","2024-07-31 12:59:59.773","2024-07-31 13:03:04.630"
"56","0","2024-07-31 13:03:04.630","2024-07-31 13:03:28.687"
"57","1","2024-07-31 13:03:28.687","2024-07-31 13:03:35.850"
"58","0","2024-07-31 13:03:35.850","2024-07-31 13:03:55.870"
"59","1","2024-07-31 13:03:55.870","2024-07-31 13:06:35.383"
"60","0","2024-07-31 13:06:35.383","2024-07-31 13:06:49.397"
"61","1","2024-07-31 13:06:49.397","2024-07-31 13:12:45.470"
"62","0","2024-07-31 13:12:45.470","2024-07-31 13:12:59.533"
"63","1","2024-07-31 13:12:59.533","2024-07-31 13:18:00.960"
"64","0","2024-07-31 13:18:00.960","2024-07-31 17:20:17.993"
"65","1","2024-07-31 17:20:17.993","2024-07-31 17:20:32.007"
"66","0","2024-07-31 17:20:32.007","2024-07-31 17:49:51.453"
"67","1","2024-07-31 17:49:51.453","2024-07-31 17:51:34.747"
"68","0","2024-07-31 17:51:34.747","2024-07-31 17:51:59.867"
"69","1","2024-07-31 17:51:59.867","2024-07-31 18:02:22.937"
"70","0","2024-07-31 18:02:22.937","2024-07-31 18:08:47.757"
"71","1","2024-07-31 18:08:47.757","2024-07-31 18:15:36.600"
"72","0","2024-07-31 18:15:36.600","2024-07-31 18:15:51.617"
"73","1","2024-07-31 18:15:51.617","2024-07-31 18:26:04.037"
"74","0","2024-07-31 18:26:04.037","2024-07-31 23:37:56.060"
"75","1","2024-07-31 23:37:56.060","2024-07-31 23:38:08.073"
"76","0","2024-07-31 23:38:08.073",
@pturmel
Very good. Notice that the first row overlaps yesterday's start of day, and the last row has a null endpoint. Time to account for that by wrapping another operation around what you have so far. New SQL for your NQ:
SELECT AGV10 As Charging,
	CASE WHEN t_stamp < :startts THEN :startts ELSE t_stamp END AS clipped_t_stamp,
	COALESCE(t_next, :endts) AS clipped_t_next
FROM (
	SELECT *,
		LEAD(t_stamp) OVER (ORDER BY t_stamp) AS t_next
	FROM ChargeTime
	WHERE
		t_stamp >= (
			SELECT TOP 1 t_stamp
			FROM ChargeTime
			WHERE t_stamp < :startts
			ORDER BY t_stamp DESC
		AND t_stamp < :endts
) clipped
ORDER BY clipped_t_stamp
New querie. How does this tie into the perspective table?
I expected you to just change the prior NQ, but you can just point the table binding at this instead.
Ohhh. Ill change the original. Just misunderstood you
Share the new dataset...
Computer crashed...... :face_with_symbols_over_mouth: ill have to re-do the view. We can pick back up another day.
When you start back up, here's the next step:
SELECT Charging,
	:startts AS PeriodStart,
	0.001 * SUM(DATEDIFF(ms, clipped_t_stamp, clipped_t_next)) AS Seconds
FROM (
	FROM (
		SELECT *,
		FROM ChargeTime
		WHERE
			t_stamp >= (
				FROM ChargeTime
	) clipped
) counted
GROUP BY Charging
ORDER BY Charging
"#NAMES"
"Charging","clipped_t_stamp","clipped_t_next"
"#TYPES"
"I","date","date"
"#ROWS","53"
"0","2024-07-31 07:00:00.000","2024-07-31 08:11:05.616"
"1","2024-07-31 08:11:05.616","2024-07-31 08:11:43.786"
"0","2024-07-31 08:11:43.786","2024-07-31 08:19:34.506"
"1","2024-07-31 08:19:34.506","2024-07-31 08:20:05.536"
"0","2024-07-31 08:20:05.536","2024-07-31 08:20:35.573"
"0","2024-07-31 08:29:07.783","2024-07-31 08:29:23.806"
"1","2024-07-31 08:29:23.806","2024-07-31 08:34:03.356"
"0","2024-07-31 08:34:03.356","2024-07-31 08:35:09.556"
"1","2024-07-31 08:35:09.556","2024-07-31 08:40:33.230"
"0","2024-07-31 08:40:33.230","2024-07-31 08:40:48.246"
"1","2024-07-31 08:40:48.246","2024-07-31 08:47:50.026"
"0","2024-07-31 08:47:50.026","2024-07-31 08:48:05.070"
"0","2024-07-31 08:48:36.110","2024-07-31 08:54:56.516"
"1","2024-07-31 08:54:56.516","2024-07-31 08:55:34.563"
"1","2024-07-31 10:02:51.380","2024-07-31 10:14:33.646"
"0","2024-07-31 10:14:33.646","2024-07-31 12:14:58.550"
"1","2024-07-31 12:14:58.550","2024-07-31 12:16:55.506"
"0","2024-07-31 12:16:55.506","2024-07-31 12:37:05.820"
"1","2024-07-31 12:37:05.820","2024-07-31 12:37:22.966"
"0","2024-07-31 12:37:22.966","2024-07-31 12:48:53.966"
"1","2024-07-31 12:48:53.966","2024-07-31 12:53:42.036"
"0","2024-07-31 12:53:42.036","2024-07-31 12:54:06.063"
"0","2024-07-31 12:58:21.620","2024-07-31 12:58:48.646"
"1","2024-07-31 12:58:48.646","2024-07-31 12:59:35.700"
"0","2024-07-31 13:03:04.630","2024-07-31 13:03:28.686"
"1","2024-07-31 13:03:28.686","2024-07-31 13:03:35.850"
"0","2024-07-31 13:06:35.383","2024-07-31 13:06:49.396"
"1","2024-07-31 13:06:49.396","2024-07-31 13:12:45.470"
"1","2024-07-31 17:20:17.993","2024-07-31 17:20:32.006"
"0","2024-07-31 17:20:32.006","2024-07-31 17:49:51.453"
"1","2024-07-31 17:49:51.453","2024-07-31 17:51:34.746"
"0","2024-07-31 17:51:34.746","2024-07-31 17:51:59.866"
"1","2024-07-31 17:51:59.866","2024-07-31 18:02:22.936"
"0","2024-07-31 18:02:22.936","2024-07-31 18:08:47.756"
"1","2024-07-31 18:08:47.756","2024-07-31 18:15:36.600"
"0","2024-07-31 18:15:36.600","2024-07-31 18:15:51.616"
"1","2024-07-31 18:15:51.616","2024-07-31 18:26:04.036"
"0","2024-07-31 18:26:04.036","2024-07-31 23:37:56.060"
"0","2024-07-31 23:38:08.073","2024-08-01 07:00:00.000"
New dataset. Havent done your last one yet
Thats getting an error.....Incorrect syntax near ')'.")
@pturmel