OPC DA with schneider PLC but have ComSubscription error

I found this: https://www.schneider-electric.com/en/faqs/FA298805/

Hello All,

I have solved my case:
https://docs.inductiveautomation.com/display/DOC79/OPC+COM#OPCCOM-IgnitionServerDCOMSettings
point 4:
4.You can also try setting the Default Authentication Level to None and the Default Impersonation Level to Identify on the Default Properties tab. This isn’t always necessary but it can sometimes help.

so on my computer it is:

and now the value can be read.
Thanks a lot for your help!