Pulse function in ignition

This is a typical momentary button. This is also a bad idea. This leaves the system open to the button getting latched on and never reset. This is also a problem with Citect. I recommend you modify the PLC logic slightly to make the PLC reset the bit after a latch from the SCADA, its much better and less error prone.