Siemens PLC troubles

Hi,

first of all, thanks for your reply. In our case, that wouldn’t be a problem, because our CPU is Siemens 317-2 PN/DP with 32 socket connections available. Currently, we have connected the following devices:

  • 4 HMIs (through PROFIBUS)
  • Ignition gateway (through Ethernet)

The problem appears when we connect another device through Ethernet (our PC with Siemens Step 7 to maintenance and programming tasks).

In our CPU configuration, we have 6 reserved channels for HMI connections, and 4 free additional channels for programming. In fact, we have 12 reserved channels for Ignition Gateway (we have tried testing with more and less channels in order to get a solution, but problems continue).

Thanks a lot
Best regards