Siemens S7-1200 tags in Ignition Edge

Got two options with Siemens, either activate the OPC Server on the PLC, and use the Ignition OPC connection, this should then let you use the tag naming to bring over the tags.

Or options 2, use the Siemens s7-1200 PLC driver, you'll then need to manually add the tags based on the offsets in a global DB, reference the document to see hwo to do this:

https://docs.inductiveautomation.com/display/DOC81/Siemens

1 Like